Thread: roll-out tripping!

  1. #1
    Join Date
    Dec 2012
    Posts
    19
    Post Likes

    Confused roll-out tripping!

    Hi guys,

    new guy on here, working on a HEIL Model # H9MPD075F12A2 that is tripping the rollout swith after watching the thing run and start many times it has become evident that there is no flame rollout it is simply overheating and it is only the right switch which mounts a little higher on the box than the left side, I have switch the switches around and it trip on the same spot. the furnace does have a little higher than normal heat rise but nothing to alarming maybe 50-60 but it is already on med-hi speed. filter clean and all registers open. pressure on the collector box is 2.80" H2O unfortunatelly cant get a reliable reading @ the burner box as its cabinet not just the box. Both intake and exhaust returned my golf ball, so not sure if I want to condem the secondary HE or is something else going on. I wish there was some data on the design static of the draft @ the collector box oddly enought I think it is related to the high heat rise but how?

  2. #2
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    Could be over-fired. Did you check gas pressures?

  3. #3
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    I used to install Heil equip. but it's been a few years since I sold any. Is this a 90+ or above furnace? Sounds like it is. Sounds like you have a leak in the burner box somewhere close the the roll out switch that's tripping. You must have a blockage of some sort in the air flow causing the high heat rise and tripping the ROS

  4. #4
    Join Date
    Oct 2012
    Location
    Danville, KY
    Posts
    348
    Post Likes
    I worked on my first goodman furnace for a friend a few months ago doing the same thing, it was a 90+. I never saw any flame rollout but it tripped when it was cold and had to run a lot overnight.

    I went down on the gas pressure to about 3" and it helped a lot but didn't fix. after cleaning the secondary and didn't get better results we changed out the heat exchanger and took care of the issue. I couldn't find a hair crack in it but I guess it had to be there though.

  5. #5
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Easy to diagnose with a combustion analyzer...

  6. #6
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by chippert View Post
    I worked on my first goodman furnace for a friend a few months ago doing the same thing, it was a 90+. I never saw any flame rollout but it tripped when it was cold and had to run a lot overnight.

    I went down on the gas pressure to about 3" and it helped a lot but didn't fix. after cleaning the secondary and didn't get better results we changed out the heat exchanger and took care of the issue. I couldn't find a hair crack in it but I guess it had to be there though.
    I would bet if you took the plate off the hot side of the secondary, you would have found a lot of rust flakes plugging some of the tubes going through the secondary.

  7. #7
    Join Date
    Oct 2012
    Location
    Danville, KY
    Posts
    348
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    I would bet if you took the plate off the hot side of the secondary, you would have found a lot of rust flakes plugging some of the tubes going through the secondary.
    There was a little junk in them. I used a 45 caliber bore to clean them. looked like need when I got done though.

  8. #8
    Join Date
    Dec 2012
    Posts
    19
    Post Likes
    Thread Starter
    I thought about that but could not make any sense why it would start all of the sudden, but that will be next probably monday!

  9. #9
    Join Date
    Dec 2012
    Posts
    19
    Post Likes
    Thread Starter
    sorry, forgot to mention that has been done the flue readings where about 89% efficiency 122F & 6.2 CO

  10. #10
    Join Date
    Dec 2012
    Posts
    19
    Post Likes
    Thread Starter
    I don't know what you mean by hot side of the secondary?? but I've inspected the collector box, I guess they are prown to cracking and while it was off all the pipes of the secondary looked pretty clean, some rust but nothing flaking off.

  11. #11
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by frustraded tech View Post
    sorry, forgot to mention that has been done the flue readings where about 89% efficiency 122F & 6.2 CO
    Need CO and O2 readings over time. Have to watch those readings over the whole run cycle. Just one set of readings taken at one point in time is almost worthless.

  12. #12
    Join Date
    Dec 2012
    Posts
    19
    Post Likes
    Thread Starter
    I don't have my notes and i forgot what the O2 was but it ran almost 45 min it started with a 92% efficiency later on dropped to the 89%, i almost thought i had it figured out because it ran so long. one important fact since i was there the first time over a week ago the unit has not tripped by a trial and error a combination of leaving the upper door on and the intake pipe off, then the unit appear to not trip, but I am having a hard time making sense of why does it help to leave the door on??? again with the door off and the pipe on it trips.

  13. #13
    Join Date
    Jan 2006
    Location
    muncie Indiana
    Posts
    664
    Post Likes
    Did you check the back of the inducer motor, to make sure the restricter plate hasn't come apart or crumbled? Ive had many of headaches over those dumb things.

  14. #14
    Join Date
    Dec 2012
    Posts
    19
    Post Likes
    Thread Starter
    yes i have, these dont have a restrictor but the do have a gasket that tends to fall apart and to center the inducer over the opening is kinda tricky but all that looks good. i was there today so read my follow up see what think that way I don't have to type it so many times.

  15. #15
    Join Date
    Dec 2012
    Posts
    19
    Post Likes
    Thread Starter
    follow up...........first of all thank you to all for your feedback it has helped me a lot. so customer called today saying he found water on the floor near the furnace and water heater, the water heater is only 2 year old and I told them I would be right over (even though its my bday) hehe, because of course I assumed that I had forgoten to tighten a clam or to put back a hose or whatever but the top of the cabinet was bone dry and the water is dripping from the rail for the blower motor and I am assuming is carrying on the rail from just under the exchanger then to the front, now could the of been a hairline crack that just open up in the secondary HE I was not able to put my Combustion analizer on it but if water is leaking the exchanger its a no brainer right??

  16. #16
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    Sounds like you have a leak in the secondary heat exchanger.

  17. #17
    Join Date
    Dec 2012
    Location
    Alabama
    Posts
    19
    Post Likes
    Sounds like the 2nd heatchamber( looks like a finned coil ) is stopped up with lint or dirt, reduces airflow, causes excesive heat, but what do i know im just armchairing here

  18. #18
    Join Date
    Dec 2000
    Location
    Victorville Ca
    Posts
    5,714
    Post Likes
    Just jumper it out and charge $495.00 . There problem solved

  19. #19
    Join Date
    Nov 2011
    Location
    USA
    Posts
    4,451
    Post Likes
    Quote Originally Posted by Roncool View Post
    Just jumper it out and charge $495.00 . There problem solved
    Bad day, huh?

  20. #20
    Join Date
    Dec 2012
    Posts
    19
    Post Likes
    Thread Starter
    that's what I was leaning towards but wanted to see if anybody had any thing similar that I could have of mis-interpreted. thank you!
    Last edited by frustraded tech; 12-10-2012 at 07:08 PM. Reason: grammar

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •