upon replacement of both exchangers there was no signs of rust or sludge build up on the socondary, also no restrictions or considerable lint or debris found on the AC coil the rings from the clam shells had busted suspect the draft inducer was pulling air from the conditioned space rather than from the intake causing the flame to run slower down the exchanger therefore heating the burner box.