yes i have, these dont have a restrictor but the do have a gasket that tends to fall apart and to center the inducer over the opening is kinda tricky but all that looks good. i was there today so read my follow up see what think that way I don't have to type it so many times.
-
follow up...........first of all thank you to all for your feedback it has helped me a lot. so customer called today saying he found water on the floor near the furnace and water heater, the water heater is only 2 year old and I told them I would be right over (even though its my bday) hehe, because of course I assumed that I had forgoten to tighten a clam or to put back a hose or whatever but the top of the cabinet was bone dry and the water is dripping from the rail for the blower motor and I am assuming is carrying on the rail from just under the exchanger then to the front, now could the of been a hairline crack that just open up in the secondary HE I was not able to put my Combustion analizer on it but if water is leaking the exchanger its a no brainer right??
-
Sounds like you have a leak in the secondary heat exchanger.
-
Sounds like the 2nd heatchamber( looks like a finned coil ) is stopped up with lint or dirt, reduces airflow, causes excesive heat, but what do i know im just armchairing here
-
Just jumper it out and charge $495.00 . There problem solved
-
 Originally Posted by Roncool
Just jumper it out and charge $495.00 . There problem solved
Bad day, huh?
-
that's what I was leaning towards but wanted to see if anybody had any thing similar that I could have of mis-interpreted. thank you!
Last edited by frustraded tech; 12-10-2012 at 08:08 PM.
Reason: grammar
-
-
Oh boy, I think he took you serious....
Worry is a really gross misuse of one's imagination. -- PHM
-
I forgot what the orinal problem was no I didn't, but I was confused about what he was talking about, it wouldn't do much for the puddle of water, either.
-
 Originally Posted by frustraded tech
follow up...........first of all thank you to all for your feedback it has helped me a lot. so customer called today saying he found water on the floor near the furnace and water heater, the water heater is only 2 year old and I told them I would be right over (even though its my bday) hehe, because of course I assumed that I had forgoten to tighten a clam or to put back a hose or whatever but the top of the cabinet was bone dry and the water is dripping from the rail for the blower motor and I am assuming is carrying on the rail from just under the exchanger then to the front, now could the of been a hairline crack that just open up in the secondary HE I was not able to put my Combustion analizer on it but if water is leaking the exchanger its a no brainer right??
Stop assuming, and check the secondary with a good mirror and flashlight. Pull that blower motor and get your head right in there. The plastic secondary connection always cracks on these.
-
plastic? you mean collector box? that was inspected and look fine at the time. why would it be dry on top if that was leaking. I have also taken the blower and looked at the secondary (before the leak) and could see much but I was actually cheching that it was no plugged not for cracks.
-
Secondary HE will be replaced customer is debating about primary since it might not be under warranty.