    You need a qualified CO expert to look at the furnace. Does the new boiler and water heater vent into the same pipe?

    You may have a new atmospheric boiler that has a draft hood. You could have such a high draft in the flue pipe which is creating a curtain/eddy effect which is making the boiler spill into the room. Your old boiler had a barometric damper with no draft hood. This made the boiler vent happily up the flue pipe. The fix to your issue would have a qualified CO/Combustion technician get rid of the draft hood and install a barometric damper with a spill switch to the new boiler and water heater.

    I would also invest in a low level CO monitor. I would turn your appliances off until then.

  2. #15
    Join Date
    Dec 2012
    Posts
    3
    Post Likes
    Thread Starter
    Thanks for the reply. There is not separate hot water heater -- it is an indirect one running off another zone. The boiler, a Burnham ES2, is atmospheric and is connected to the existing, relined chimney. The flue damper is motorized. Since I have left the door to the utility area open I have had a zero reading on my new CO detector and zero from the fire department's more sophisticated one.

    Quote Originally Posted by gravity View Post
    You need a qualified CO expert to look at the furnace. Does the new boiler and water heater vent into the same pipe?

    You may have a new atmospheric boiler that has a draft hood. You could have such a high draft in the flue pipe which is creating a curtain/eddy effect which is making the boiler spill into the room. Your old boiler had a barometric damper with no draft hood. This made the boiler vent happily up the flue pipe. The fix to your issue would have a qualified CO/Combustion technician get rid of the draft hood and install a barometric damper with a spill switch to the new boiler and water heater.

    I would also invest in a low level CO monitor. I would turn your appliances off until then.

  3. #16
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    4,972
    Post Likes
    Th potential for trouble still exists if something as simple as closing a door gives rise to generating carbon monoxide.
    DO NOT TAKE YOUR SAFETY FOR GRANTED.
    You need to have your system inspected by someone trained in combustion analysis to provide a permanent solution.

  4. #17
    Join Date
    Apr 2013
    Posts
    7
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 04-24-2013 at 04:58 PM. Reason: Non Pro * Member

  5. #18
    Join Date
    Aug 2012
    Location
    North Dakota
    Posts
    522
    Post Likes
    another thing is a co detector relies on humidity to carry the co to the detector!!!!

  6. #19
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,898
    Post Likes
    pwilliams, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Your post has been deleted.
    Further infractions may result in loss of posting privileges.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #20
    Join Date
    Apr 2013
    Posts
    7
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 04-25-2013 at 07:03 PM. Reason: Non Pro * Member, no warning for apologizing

  8. #21
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,898
    Post Likes
    Quote Originally Posted by pwilliams View Post
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Nope, not even allowed to apologize in someone else's thread. Please don't respond again.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 2 of 2 FirstFirst 12

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.