Page 1 of 4 1234 LastLast
Results 1 to 13 of 41

Hybrid View

  1. #1
    Join Date
    Dec 2011
    Location
    Hiram, Ohio
    Posts
    291
    Post Likes

    2 stage AC or heat pump?

    This spring, had a new modulation propane furnace installed, using my central AC system that has been in place since 1999. So far, I just love the new furnace! And the installer addressed some air flow restriction issues on my return line so the AC worked better this summer. But, the AC system had a few minor breakdowns over the summer, due to age. I am thinking about replacing the AC system early this spring, to avoid a total failure right when I need it most.
    The cost difference between a 2-stage AC and a 2-stage heat pump is not that much, and I am seriously considering going with the heat pump to have a hybrid heating system, which I think will pay off considering the cost of propane! Question is this: My old AC was just a nice bare-bones workhorse.. simple contactor that fired up the compressor and condenser fan.. Not a lot of stuff to break. A heat pump would be more complicated.. therefore more stuff to fail. So my question is long term should I go for the heat pump or just an AC system? Thanks, Mike

  2. #2
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    37,393
    Post Likes
    First: We really need to know where you live; city/state or close to a larger city/state is fine. Climate conditions are important to your question. Example: In northern climates where AC is only a mos or so... 2 stage AC (16 or 18 or 20 SEER) is not worth it. However in an 'oven climate' like Phoenix it is definitely worth it. Contrary to some sales folks opinion , higher than 16 SEER AC in my area (Atlanta), it is hard to re-coup one's investment. If you are approaching this for the heat value more than the cooling value; then using 2 stage equipment and over sizing one step (AC adequate in low stage) will give you more heat capacity to a lower outdoor temp. For folks reading this thread; he already has a VS drive furnace (the modulating furnace); one should ALWAYS have a VS drive furnace or air handler when approaching higher efficiency equipment.

    Since you are restricted to LP gas for heating, setting up a dual-fuel system is a good idea... LP is expensive and LP furnaces tend to need more maintenance... LP is a dirty fuel and causes issues with equipment. The less time running that LP furnace, the better on both issues.

    Might want to remember a HP runs year round; so normal wear on components will shorten its life compared to straight AC. Two stage equipment is not that complicated, however it does require more maintenance (cleaning and filter changes). I would recommend a media style air filter if you do not already have one. Also, you will need some form of DF (dual-fuel) controller; lots of high end thermostats can handle this issue.

    Post your location... we can help more knowing the climate.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    39,010
    Post Likes
    With propane heat, I'd certainly be thinking of a heat pump. Personally I'd stay a good single stage.

  4. #4
    Join Date
    Jan 2009
    Location
    Saint Joseph, MI
    Posts
    5,564
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    With propane heat, I'd certainly be thinking of a heat pump. Personally I'd stay a good single stage.

    +1. IF you have propane, dual fuel all the way for sure. The effciency of heat pumps is actually slightly lower in 1st stage, so you don't gain much with 2 stage. 2 stage is more for comfort and effciency in cooling than heating.

  5. #5
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    2,576
    Post Likes
    Quote Originally Posted by motoguy128 View Post
    +1. IF you have propane, dual fuel all the way for sure. The effciency of heat pumps is actually slightly lower in 1st stage, so you don't gain much with 2 stage. 2 stage is more for comfort and effciency in cooling than heating.
    I assume you mean 1st stage(low stage) is HIGHER efficiency, all equipment that I have seen shows much higher COP ratings.
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  6. #6
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,744
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    With propane heat, I'd certainly be thinking of a heat pump. Personally I'd stay a good single stage.
    I agree with B.L., EXCEPT, I would go with the 2-stage H/P. No offense, B.L.!

  7. #7
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,368
    Post Likes
    +2, I've got a single stage 14 SEER HP on our office 95% LP furnace. Works fine. With the variable speed gas you can probably get 15 SEER in single stage HP. Lots less complex controls in a single speed HP. Check with your electrical supplier for special pricing on electricity if have a HP. Ours discounts it @40% during winter with HP.

  8. #8
    Join Date
    Dec 2011
    Location
    Hiram, Ohio
    Posts
    291
    Post Likes
    Thread Starter
    Thanks for the replies... I live in rural NE Ohio.. The AC is in use probably 3 months out of the year, but it is needed, we get some brutal humidity! I wasn't sure if I was allowed to mention brand names, but I have a 96% 80K modulating furnace, I had the big filter installed with it (something like 6" thick?) and the t-stat is the best one I could get, full-communicating so once I have this AC/HP in place I can tell it when to lock out the propane, etc.. I really like the system. BTW, on a really hot sunny humid day (like 98 deg) with the kids going in and out of the house the 3-ton AC will run almost continuously, so I think that is just about the correct size. Thanks!

  9. #9
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    37,393
    Post Likes
    THX for the location... helps.

    Two stage comes in even ton sizes... so a 3 ton will be around 2 ton low... and a 4 ton will be around 2-3/4 ton low.

    If you have a communicating T-stat from the same manufacturer of the furnace, you are most of the way towards a really nice system. Personally, I would go ahead with 16 SEER 2 stage HP, and would go with 4 tons. On the AC side low will cover most of your needs, with the high available for a really HOT day or load (think party with doors never closing). You would get the added HP capacity for the winter, with some reserve AC for the summer. And the VS drive furnace with its dehumidification cycle will cover mild over-capacity of AC. Note you probably will need a new lineset (copper tubes) from the inside to the outside. Have the HVAC guy look at the ductwork to be sure it will handle the 4 tons of airflow. Sometimes I mount a 5 ton coil with a 4 ton HP (did that a few weeks ago) in your situation... tends help the HP and the AC dehum cycle also (some would disagree with dehum, works on my installs).

    Just curious, what brand of equipment?

    Hope this helps.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

  10. #10
    Join Date
    Dec 2011
    Location
    Hiram, Ohio
    Posts
    291
    Post Likes
    Thread Starter
    goodman.. with the comfortnet.

  11. #11
    Join Date
    Jan 2009
    Location
    Saint Joseph, MI
    Posts
    5,564
    Post Likes
    How many of those have you installed? How have they performed? The heating performance of their heat pumps are very good without having to massively oversize indoor coils

    Sent from my DROID RAZR using Tapatalk 2

  12. #12
    Join Date
    Nov 2012
    Posts
    48
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 12-07-2012 at 06:07 PM. Reason: Non Pro * Member

  13. #13
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    37,393
    Post Likes
    Quote Originally Posted by Quantumstate View Post
    How about with Trane? For a dual-fuel system with 3 ton HP would it be useful to go with a 4 ton coil?
    Need access to the AHRI matches. If your contractor does not even know what those are.... well what are the chances of a quality install? Remember: Installation is more important than brand of equipment.