    Hi all..Can anyone please explain me the concept of delta T & what delta T shall be considered for Chillers, Ahu & district cooling systems?
    And how it shall be calculated and considered?

    Regards

  2. #2
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Thread relocated to AOP

  3. #3
    Join Date
    Dec 2011
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by Chris_Worthington View Post
    Thread relocated to AOP
    What is AOP?

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by mohsinrkhan86 View Post
    What is AOP?
    Ask Our Pros.

  5. #5
    Join Date
    Dec 2012
    Location
    Houston
    Posts
    3
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 12-08-2012 at 09:58 AM. Reason: Non Pro * Member

  6. #6
    Join Date
    Dec 2011
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by Catherin View Post
    District cooling systems can replace any type of air conditioning system, but primarily compete with air-cooled reciprocating chiller systems serving large buildings which consume large amounts of electricity.
    But what are delta T values for different systems to consider?

  7. #7
    Join Date
    Dec 2012
    Location
    Houston
    Posts
    3
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 12-08-2012 at 09:59 AM. Reason: Non Pro * Member

  8. #8
    Join Date
    Dec 2011
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by Catherin View Post
    A delta-T is the change in temperature of a single substance or flow of substance. The evaporator delta-T is the temperature difference between the air entering the coil and the air leaving the coil.
    Yeah i know what delta T is. But i heard that there are pre-specified values of delta T for different types of systems like ahu, chiller etc

  9. #9
    Join Date
    Dec 2012
    Location
    Houston
    Posts
    3
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 12-08-2012 at 10:00 AM. Reason: Non Pro * Member

  10. #10
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,186
    Post Likes
    Quote Originally Posted by mohsinrkhan86 View Post
    Yeah i know what delta T is. But i heard that there are pre-specified values of delta T for different types of systems like ahu, chiller etc
    Yes, there are specific Delta T parameters that are engineered into any given equipment.

    I've seen reach in coolers designed for 5 degrees delta for a specific purpose. I've seen chillers run from 10 to 20 degrees delta T, as well as air handlers. you will have to research each individual piece of equipment to find what the design Delta T is soposed to be.

    ...Ron
    Roof Rat

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Catherin, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Your post has been deleted.
    Further infractions may result in loss of posting privileges.

  12. #12
    Join Date
    Dec 2011
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by rscamaro View Post
    Yes, there are specific Delta T parameters that are engineered into any given equipment.

    I've seen reach in coolers designed for 5 degrees delta for a specific purpose. I've seen chillers run from 10 to 20 degrees delta T, as well as air handlers. you will have to research each individual piece of equipment to find what the design Delta T is soposed to be.

    ...Ron
    Thanx rscamaro for your response.
    Another doubt, more the delta T value, better is the system. Is it true?

  13. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by mohsinrkhan86 View Post
    Thanx rscamaro for your response.
    Another doubt, more the delta T value, better is the system. Is it true?
    Not necessarily.



  14. #14
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    The question you have is incredibly complex. There is no "20 degree drop and it's good" type thing anymore. There's so much going into it from the design, flow requirements of chilled water, air volume, air temperature and humidity that unless you ask a very specific question with some other data/model numbers we aren't going to able to assist you.

  15. #15
    Join Date
    Dec 2011
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by ryan1088 View Post
    The question you have is incredibly complex. There is no "20 degree drop and it's good" type thing anymore. There's so much going into it from the design, flow requirements of chilled water, air volume, air temperature and humidity that unless you ask a very specific question with some other data/model numbers we aren't going to able to assist you.
    Ok thanx for yur helpful response.
    I asked this question as i heard that delta T for district cooling system shall be around 14-16, whereas the value for chiller is 12.
    How do we calculate delta T for a system. Formula for it?
    I know a formula,
    Gpm/Tr = 24/delta T
    But then, how to calculate gpm for a system, cuz i knew Tr=2.4*gpm, but then i came across a system where the relation was Tr=1.8*gpm.
    Please clarify if possible.

  16. #16
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    "Delta", as used here, simply means "difference", or "differential". So, "delta T" is simply the temperature difference. In this case, the temperature difference of a medium (water or air, for example) as it flows thru a heat exchanger. As you can see, delta T is measured rather than calculated. As far as what it should be, that is best learned by finding the design specifications of the system. Each component in a system was selected to perform a specific function, under specific conditions - or range of conditions. To best determine if those components are operating correctly you need to know the design conditions, then operate the system at those conditions, and measure all parameters while operating at those design conditions. Then compare the measurements with the design specifications.

  17. #17
    Join Date
    Dec 2001
    Posts
    1,365
    Post Likes
    oops

  18. #18
    Join Date
    Dec 2011
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by Nuclrchiller View Post
    "Delta", as used here, simply means "difference", or "differential". So, "delta T" is simply the temperature difference. In this case, the temperature difference of a medium (water or air, for example) as it flows thru a heat exchanger. As you can see, delta T is measured rather than calculated. As far as what it should be, that is best learned by finding the design specifications of the system. Each component in a system was selected to perform a specific function, under specific conditions - or range of conditions. To best determine if those components are operating correctly you need to know the design conditions, then operate the system at those conditions, and measure all parameters while operating at those design conditions. Then compare the measurements with the design specifications.
    Who is going to select the design specifications?

  19. #19
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    The enginneering department which requires enginnering degrees (pun) which it sounds like you are headed. Sometimes too much info too soon can be dangerous.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •