Results 14 to 19 of 19
-
12-08-2012, 02:39 PM #14
The question you have is incredibly complex. There is no "20 degree drop and it's good" type thing anymore. There's so much going into it from the design, flow requirements of chilled water, air volume, air temperature and humidity that unless you ask a very specific question with some other data/model numbers we aren't going to able to assist you.
-
12-08-2012, 02:50 PM #15
Regular Guest
- Join Date
- Dec 2011
- Posts
- 30
Ok thanx for yur helpful response.
I asked this question as i heard that delta T for district cooling system shall be around 14-16, whereas the value for chiller is 12.
How do we calculate delta T for a system. Formula for it?
I know a formula,
Gpm/Tr = 24/delta T
But then, how to calculate gpm for a system, cuz i knew Tr=2.4*gpm, but then i came across a system where the relation was Tr=1.8*gpm.
Please clarify if possible.
-
12-10-2012, 09:38 AM #16
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105
"Delta", as used here, simply means "difference", or "differential". So, "delta T" is simply the temperature difference. In this case, the temperature difference of a medium (water or air, for example) as it flows thru a heat exchanger. As you can see, delta T is measured rather than calculated. As far as what it should be, that is best learned by finding the design specifications of the system. Each component in a system was selected to perform a specific function, under specific conditions - or range of conditions. To best determine if those components are operating correctly you need to know the design conditions, then operate the system at those conditions, and measure all parameters while operating at those design conditions. Then compare the measurements with the design specifications.
-
12-12-2012, 05:32 PM #17
oops
-
12-18-2012, 02:24 PM #18
Regular Guest
- Join Date
- Dec 2011
- Posts
- 30
-
12-18-2012, 02:41 PM #19
The enginneering department which requires enginnering degrees (pun) which it sounds like you are headed. Sometimes too much info too soon can be dangerous.