    Confused connecting power to heat strip

    I have a HKR-20C strip for Goodman 4 ton package heat pump. The instructions are not real clear about connecting power.
    Says connect to terminal blocks. DO I use a jumper from block 1 to block 3 then 2 to 4?

  2. #2
    Join Date
    Oct 2008
    Location
    Indianapolis
    Posts
    172
    Post Likes
    No

  3. #3
    Join Date
    May 2012
    Posts
    21
    Post Likes
    Thread Starter
    I only have two power wires for the 240v

  4. #4
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    High voltage is dangerous so dangerous, Do not attemp install or repair without calling a reputable hvac company.

  5. #5
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    This is not a DIY forum. We can't help you with this. Sorry

  6. #6
    Join Date
    May 2012
    Posts
    21
    Post Likes
    Thread Starter
    I got a Professional to install..I get home from work, now fan runs all the time..bad luck for me

  7. #7
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Quote Originally Posted by man00 View Post
    I got a Professional to install..I get home from work, now fan runs all the time..bad luck for me
    Just because you got a company to install it does not mean it is proffesional. With that lets say it was done proffesionally things do go wrong with equipment so why would you try to repair it by yourself? It should be under warranty by instal company.

  8. #8
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    make sure your"Fan" setting on thermostat is not set to "ON" instead of "AUTO". If it's on "ON" then the fan will run continuously.

  9. #9
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    hope they installed 2 60 amp services .

  10. #10
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by toocoolforschool View Post
    Just because you got a company to install it does not mean it is proffesional. With that lets say it was done proffesionally things do go wrong with equipment so why would you try to repair it by yourself? It should be under warranty by instal company.
    +1

  11. #11
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by man00 View Post
    I have a HKR-20C strip for Goodman 4 ton package heat pump. The instructions are not real clear about connecting power.
    Says connect to terminal blocks. DO I use a jumper from block 1 to block 3 then 2 to 4?
    If your unsure about the way your contractor installed something, you can post a picture of it, and we can tell you if it was installed correctly.

    We cannot help you DIY this though. If the point of your vist is to fix it yourself, then your out of luck. Do not expect any steps in fixing any problem, other than to call your installing contractor.

    What I will say, is there are certain applications where what it seems your describing is allowed, provided certain parts are used.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  12. #12
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    20 KW? ??

    Hope your electric meter is bolted down so it doesn't spin off the wall!

  13. #13
    Join Date
    May 2012
    Posts
    21
    Post Likes
    Thread Starter
    all is fine now..the strip was wired wrong from factory..

  14. #14
    Join Date
    May 2012
    Posts
    21
    Post Likes
    Thread Starter
    Thanks for the help all

  15. #15
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by man00 View Post
    all is fine now..the strip was wired wrong from factory..
    Highly doubtfull, to be honest.

    I've put in hundreds of hkr heat kits, over a period of 8 years. I've never seen one wired wrong from the factory. Plus, the heat kit doesn't control fan operation.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  16. #16
    Join Date
    May 2012
    Posts
    21
    Post Likes
    Thread Starter
    I don't know just going by what the install guy said..something about L1 and L 2 crossed

  17. #17
    Join Date
    May 2006
    Location
    Austin, Texas
    Posts
    800
    Post Likes
    I don't know just going by what the install guy said..something about L1 and L 2 crossed

    Huh??

  18. #18
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Quote Originally Posted by man00 View Post
    all is fine now..the strip was wired wrong from factory..
    What? That's a good one.

  19. #19
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by SBKold View Post
    20 KW? ??

    Hope your electric meter is bolted down so it doesn't spin off the wall!

    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  20. #20
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by hvacvegas View Post
    Highly doubtfull, to be honest.

    I've put in hundreds of hkr heat kits, over a period of 8 years. I've never seen one wired wrong from the factory. Plus, the heat kit doesn't control fan operation.
    +1 ........No one ever wants to take the blame now days, it's an epidemic, especially with our kids, well at least my kids.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •