multi-city units
I need to recover and weigh in the charge on 3 city multi units tomorrow. Is there a way to pump the systems charge into the condenser to make recovery easier? What would be the best way to do this job. thanks
-
12-06-2012, 08:21 PM #2
I haven't had much experience with the city multi units. I would suggest calling Mitsubishi tech support with any questions regarding these systems. 678-376-2900. You may also be able find information @ www.mylinkdrive.com.
-
12-06-2012, 10:06 PM #3
Regular Guest
- Join Date
- Jun 2012
- Posts
- 33
Thats what i figured i would do, just thought i might get a heads up before i get down there. thanks for the reply
-
12-06-2012, 11:27 PM #4
Professional Member
- Join Date
- Aug 2012
- Location
- Gainesville, FL
- Posts
- 227
Mitsubishi isn't very helpful unless you've been to their seminar or your company is approved or certified or whatever they call it. On the last few we've done we've removed refrigerant to a recovery cylinder and weighed back in from there. No special technique.
-
12-07-2012, 09:05 PM #5
Regular Guest
- Join Date
- Jun 2012
- Posts
- 33
well, i recoverd two units today. the first was 20 pounds over charged the second was 33 pounds under charged pulled a vacuum on that one and it was holding for about an hour, pressurized it to 500 psi with nitrogen till monday. i hope it holds. dont really want to leak check this mess
-
12-10-2012, 01:12 AM #6
How did your units get overcharged or undercharged? I just finished installing 3 citymulti units they made me measure my liquid line by length and size so they can provide me with the amount of refrigerant needed. We kinda got it easy though my company hasnt sent any techs to get the start up training. So Mitsubishi did the start up for us on all three units. So far ive had nothing but luck with these units. 3 years ago i installed 2 citymulti units and never had one service call.
RTFM!!!
-
12-10-2012, 08:00 PM #7
Regular Guest
- Join Date
- Jun 2012
- Posts
- 33
we're not the installing company. got called in to fix somebodys problem. Im not sure how many people have been here but we are trying to make it right.
-
12-31-2012, 11:02 AM #8
Regular Guest
- Join Date
- Mar 2012
- Location
- Georgia
- Posts
- 20
Just use a good recovery machine & keep recovery tanks cool.
-
12-31-2012, 11:10 AM #9
Regular Guest
- Join Date
- Mar 2012
- Location
- Georgia
- Posts
- 20
I have installed 3 of the City Multi systems- a great tip is to inventory your refrigerant tubing (lengths) & save the unused pieces from each branch line. Measure those left over pieces & subtract to get a very accurate line length. I have use this method & weighed in charge, have never had any issues on any of the jobs. Oldest system still working installed in 2004! These are great systems only if installed properly, follow good refrigeration practices & they'll be very dependable.
-
12-31-2012, 11:33 AM #10
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,298
Mini's, including single head, multi-head, and systems designed for many multi-heads... are ALL--VERY sensitive to charge... it is part of how they work. The 'rule of thumb' stuff we did/do with conventional split systems does NOT work.
Cleanliness is important!
Hmmm... I realize we are talking about a large amount of refrigerant... however if many folks have worked on the system... do we have any way to know if it has been contaminated with N2, air, wrong refrigerants, poor vacuum procedures, etc? If it were me, I would sell the owner on NEW refrigerant. If so, standard practices of cleanliness in leak check and triple evac would be my approach.
If you are going to re-use the refrigerant: Pull a vacuum on a CLEAN recovery cylinder. When you start to pull your charge, flush out your hoses, gauge set, cooling coil, etc. Be sure ONLY refrigerant gets into the recovery cylinder. I would err on the side of releasing a 'deminimus amount' of refrigerant... rather than chancing any inert gasses. Pull the charge down to almost zero. \
At this point do your leak check if you are going to.
Then carefully pull a thorough vacuum to specs. I go for at least 250 Microns most of the time. Remember to measure your microns at the unit, not at the gauge set or pump.
CAREFULLY calculate the charge and recharge... being careful your scale is not affected by things like hose weight and bumping.
ACCURACY is the most import thing here...
GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
12-31-2012, 12:00 PM #11
Regular Guest
- Join Date
- Mar 2012
- Location
- Georgia
- Posts
- 20
Use a high quality electronic vacuum gauge (not your $100 variety). Gotta trust your tools!
-
01-01-2013, 11:57 PM #12
Professional Member
- Join Date
- Dec 2012
- Location
- Birmingham, AL
- Posts
- 37
Been through the City Multi training course. They have a design program where you "build" your system with available components. It will give you exact weigh in charge and liquid and suction line sizes. I like to recover, and weigh in virgin refrigerent.
Also, if you want to troubleshoot a city multi system, you will need the mitsubishi "box" and a laptop, and place your clips on the data circuit between components. The "box" is pricey, I think about $400. The rig will give you the diagnosis.
-
01-03-2013, 11:13 PM #13
Regular Guest
- Join Date
- Apr 2008
- Location
- West Coast
- Posts
- 18
If your concerned about a leak best bet it to focus on BC controller flare fittings will leak if a torque wrench is not used. If isolation valves were used at BC check schrader cores. Most checks I find oil present.