Page 1 of 2 12 LastLast
Results 1 to 13 of 17

Thread: POE Oil

  1. #1
    Join Date
    Apr 2010
    Location
    Richmond, Virginia
    Posts
    296

    POE Oil

    On a small system using R22 when installing new compressor that comes with POE Oil do you have to drain it out and put Minerial oil back in ?

    Thanks

  2. #2
    Join Date
    Feb 2008
    Location
    California
    Posts
    1,893
    You don't HAVE to.

  3. #3
    Join Date
    Apr 2010
    Location
    Richmond, Virginia
    Posts
    296
    Quote Originally Posted by NANOTECH View Post
    On a small system using R22 when installing new compressor that comes with POE Oil do you have to drain it out and put Minerial oil back in ?

    Thanks

    Thanks Phase I was not sure if you could use POE Oil with R22 !!

  4. #4
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,000
    Nope. Don't have too. I usually do but I'm silly about such things.

  5. #5
    Join Date
    Sep 2008
    Posts
    501
    My understanding is POE work just fine with r-22 in m/t&h/t systems, low temp will have oil return issues. Never tested first hand, YMMV.

  6. #6
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    2,308
    22 does just fine with POE. R22 as a low temp is a different animal and requires a demand cooling module to keep discharge temperatures down. As far as issues with oil return, I have 2 condensers (1 freezer) that are low temp 22 that I take care of. I haven't noticed any problems with it.

    JP will be along here soon to tell me I'm wrong. :grin:

  7. #7
    Join Date
    Feb 2008
    Location
    California
    Posts
    1,893
    POE and R-22 is indifferent to MT or LT, it works on both.

    LT R-22 requires de-superheating to keep discharge temperatures down. Weather it be Demand Cooling or Liquid injection.

  8. #8
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,954
    Quote Originally Posted by Phase Loss View Post
    POE and R-22 is indifferent to MT or LT, it works on both.

    LT R-22 requires de-superheating to keep discharge temperatures down. Weather it be Demand Cooling or Liquid injection.

    This is the correct answer.

    Actually, if you took a brand new, R-22 low temp system today, I would prefer to use POE oil in it.

    As a synthetic oil, it is PROBABLY more temperature resistant than the mineral oil of the past.

    Oil return is as much a function of proper piping design as it is a function of refrigerant and oil

  9. #9
    Join Date
    Jan 2005
    Location
    texas
    Posts
    110
    What type of oil the system was in the original compressor? If mineral I would drain the poe from the new comp and replace with mineral then install. I will not deliberately mix those oils in large quantities.

  10. #10
    Quote Originally Posted by jpsmith1cm View Post
    This is the correct answer.

    Actually, if you took a brand new, R-22 low temp system today, I would prefer to use POE oil in it.

    As a synthetic oil, it is PROBABLY more temperature resistant than the mineral oil of the past.

    Oil return is as much a function of proper piping design as it is a function of refrigerant and oil
    Sporlan just told us from their testing POE does resist breakdown better at high temps.

  11. #11
    Join Date
    Apr 2002
    Location
    Ann Arbor, MI
    Posts
    2,945
    Quote Originally Posted by Freightshaker View Post
    Sporlan just told us from their testing POE does resist breakdown better at high temps.
    POE oil can tolerate higher temperatures than AB or mineral oils. But it suffers hydrolysis in the presence of moisture. A diatribe of mine while employed at a former employer of mine on this subject: http://sporlanonline.com/November%20...Cold%20WAR.pdf
    The greater danger for most of us lies not in setting our aim too high and falling short; but in setting our aim too low, and achieving our mark. – Michelangelo

    There are powers inside of you which, if you could discover and use, would make you everything you ever dreamed or imagined you could become. – Orison Swett Marden

    Education is what remains after one has forgotten what one has learned in school. – Albert Einstein

  12. #12
    Join Date
    Jun 2003
    Posts
    3,640
    I would leave the POE in and make a note of it on the unit.

    Then if it needs service in the future, you'll be ready for any number of alternative refrigerants that require a partial oil change.

  13. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    14,481
    Andy, I miss the Cold War emails.