    titus vav box heat issue
    im new to the vav game< i have a titus vav box, non fan powered 3 stage heat, controller is calling for 100% heat, no control voltage to contactors. line voltage is there and transformer is good. my question is: does the control board send signal to the transformer to on the secondary side to power the contactors. all the safetys are made but still no power? i guess I'm asking how does the controller send the call to the transformer?
    Jul 2003
    Orange County N.Y.
    It doesn't send a call to the transformer. The BMS system sends a signal to a control, the control sends a signal to a relay, which closes a set of points, which activate something. Transformers are usually in VAV boxes to power whatever board the operating system uses.
    I read your post as the controller (VAV box) not communicating with the BMS.
    ...Ron
    Roof Rat
    Dec 2010
    Downingtown, PA
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
    You can find the rules for posting and qualifications here.
    Additional infractions may result in loss of posting privileges.
    captaincallback