Results 1 to 13 of 30
Thread: Calculating GPM
-
12-06-2012, 04:32 PM #1
New Guest
- Join Date
- Dec 2012
- Posts
- 3
Calculating GPM
Hello all. New to the site, been in the trade about 15 years. Got a new employer, and we do work on chillers ( air cooled screw, scroll, and recip). How do you know you have proper water flow (gpms) through a chiller?How do you know what it's supposed to be? I appreciate feed back. I tried to do a search on here, but came up empty.
-
12-06-2012, 05:30 PM #2
The iom manuals of the machine will tell you the design gpm, minimum and maximum for that particular machine. At the machine using the same gauge to measure supply and return pressure with the chiller at full load, you apply this formula:
Gpm across barrel
Gpm (actual)=design gpmx(square root of actual divided by design)
A=234 x sq rt of 4/6
-
12-06-2012, 06:32 PM #3
2.5 gpm per ton for chilled water
look at your pumps and read gpm and head
if pump is correct and gpm is correct
find out what the pressure drop through the chiller is supposed to be
if it is correct
then
use
gpm x 500 x delta t
this should get you close
then you will have to learn approach.
frankI WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!
-
12-06-2012, 06:35 PM #4
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
A lot of Ioms will have a graph to assist you in calculating GPM.
Design can vary per application .
There are rules of thumb.
There are math calculations to perform .
I'll look around and see if I can come up with something for you....mikeacman
-
12-06-2012, 07:21 PM #5
-
12-06-2012, 11:24 PM #6
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 282
Here it is.
-
12-06-2012, 11:36 PM #7
New Guest
- Join Date
- Dec 2012
- Posts
- 3
You guys are awesome. Thanks for the replies.
-
12-06-2012, 11:40 PM #8
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 282
Take a look at this.
-
12-10-2012, 05:54 PM #9
-
12-10-2012, 06:40 PM #10
-
12-10-2012, 06:45 PM #11
-
12-10-2012, 06:50 PM #12
-
12-10-2012, 06:53 PM #13I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!


Reply With Quote