    Commercial refrigerator stops cooling after a few hours...

    Got call for commercial refrigerator which was not working correctly..
    1/2 ton hermetic compressor with 17oz of R134a running on 110


    Here is what I did..

    Checked outlet power.....OK, the evaporator fans were running but compressor was not running, there was no cooling...
    Checked compressor/condenser was extremely dirty, I cleaned it thoroughly...
    Ohm and ground test on compressor showed it was fine...
    The thermostat was off so I set the to 35 and the unit started cooling, it hit 37 inside and kept it for a couple of hours..
    I had to go so I Left it running, came back another 2 hours later and the unit was hitting 60 inside..

    Once again the evap fans were running but the compressor wasn't..
    I checked the power coming from the relay that's between thermostat and compressor and nada... the compressor was not getting any juice... so I checked the thermostat to see if maybe someone had touched but it was still how I left it...
    I moved the temperature up to 80 then down to 10 and after a few seconds the compressor kicked in...

    does that mean I have a bad thermostat?

    Name:  thermostat.jpg
Views: 441
Size:  27.2 KB

  2. #2
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    1,758
    Thats one h*** of a differential if not!


    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  3. #3
    Join Date
    Jul 2012
    Location
    Kansas
    Posts
    78
    What was the voltage across the thermostat terminals?

  4. #4
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,596
    I hate those thermostats......

  5. #5
    Join Date
    Sep 2011
    Posts
    58
    Well ... Xgive my stupidity, I will from now on be as precise as possible in explaining my situations with the terminology in which all non-contributing contributors feel most comfy with... Oh no wait, what the H.... for?? I mean after all, I am sure that then they will find another "flaw" and then they will just take it from there... Yah, I mean dang, why bother even answering a question when I can spend my valuable time shi###ing all over the other guys' posts...

    Happy Holidays ppl!!!

  6. #6
    Join Date
    Jan 2010
    Posts
    6,841
    Let's try this again. What type of cooler are you working on ? From the looks of your picture that is not the correct temperature control.

  7. #7
    Join Date
    Jul 2009
    Location
    saint cloud fl
    Posts
    5

    more info,

    what was youre amp draw while in operation, also what bout the thermostat its self, how were the contacts,where they open when the unit was supposed to be in operation, where was the sensing bulb located, or was the compressor open on overload....?

  8. #8
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Troubleshooting a thermostat is basic HVACR 101. The switch is either open or closed. What was the temp of the compressor shell when you got back or when the comp shuts off?

  9. #9
    Join Date
    Jul 2009
    Location
    saint cloud fl
    Posts
    5

    yep....!

    Well there is alot of people who dont even think about the thermostat....
    Quote Originally Posted by welling service View Post
    Troubleshooting a thermostat is basic HVACR 101. The switch is either open or closed. What was the temp of the compressor shell when you got back or when the comp shuts off?

  10. #10
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    1,758
    X2 on temp control
    Check for voltage across terminals. If 120 is present with warm box, replace with proper cold control!!!

    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  11. #11
    Join Date
    Jul 2012
    Location
    Kansas
    Posts
    78
    Quote Originally Posted by myhvacx View Post
    Well ... Xgive my stupidity, I will from now on be as precise as possible in explaining my situations with the terminology in which all non-contributing contributors feel most comfy with... Oh no wait, what the H.... for?? I mean after all, I am sure that then they will find another "flaw" and then they will just take it from there... Yah, I mean dang, why bother even answering a question when I can spend my valuable time shi###ing all over the other guys' posts...

    Happy Holidays ppl!!!
    I don't see anyone doing any post pooping. I do see the OP getting bent out of shape for no reason.

    You asked if the thermostat was bad, a simple voltage check would provide the answer.

  12. #12
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    1,758
    I remember not too long ago I used the likes of this forum, and my phone, as a crutch in troubleshooting.
    In realization of this, I started hesitating before dialing/typing. I became a better tech by forcing myself to go through the fundamentals of troubleshooting through my head.
    My first troubleshooting technique.......... hesitation



    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  13. #13
    Join Date
    Mar 2002
    Location
    fort walton beach fl.
    Posts
    790
    From the OP, Its sounds like the thermostat is bad. But again, I simple voltage check will confirm. The box looks like a true cooler. In that case, I would install the OEM constant cut in thermostat.
    http://acfwb.com/

    "The best preparation for good work tomorrow is to do good work today"

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event