Results 1 to 9 of 9
  1. #1
    Join Date
    Dec 2012
    Posts
    2
    Post Likes

    I am a student and need some help please

    A service technician is charging an air-conditioning system that has a TXV as the metering device using the subcooling method of charging.
    The high-side saturation teperature is 110 degrees farenhieght and the unit's technical manual specifies 10 degrees farenhight of liquid subcooling.
    What would the desired liquid-line temperature be at the condensing unit. I am totaly stuck yall!

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes

  3. #3
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,210
    Post Likes
    I think this exercise is trying to get you comfortable with these terms and how simple the solution actually is.

    So lets start with a question. What is your understanding of what liquid subcooling is?

  4. #4
    Join Date
    Nov 2012
    Location
    PA
    Posts
    56
    Post Likes
    I think he is currently taking a test.

  5. #5
    Join Date
    Feb 2012
    Location
    EVERYWHERE
    Posts
    236
    Post Likes
    I think he failed a test.

  6. #6
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Do you just want the answer or do you want us to help you figure it out?

  7. #7
    Join Date
    Dec 2012
    Location
    nc
    Posts
    7
    Post Likes
    100 degrees

  8. #8
    Join Date
    Dec 2012
    Posts
    2
    Post Likes
    Thread Starter
    I thought 100 degrees was right but I wasnt sure. I was working on some review questions out of my book, and that one just had me totally stumped. Thanks everybody!

  9. #9
    Join Date
    Apr 2012
    Location
    Texas
    Posts
    213
    Post Likes
    TXV means you will get constant superheat ...
    which means you want to fill the condenser just enough to guarantee a liquid seal at the metering device(txv)
    110 - 10 = 100 degrees to get the manufacturers requirement.
    Economy - Quality - Speed <---- pick two

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.