I am a student and need some help please
A service technician is charging an air-conditioning system that has a TXV as the metering device using the subcooling method of charging.
The high-side saturation teperature is 110 degrees farenhieght and the unit's technical manual specifies 10 degrees farenhight of liquid subcooling.
What would the desired liquid-line temperature be at the condensing unit. I am totaly stuck yall!
-
12-06-2012, 04:01 PM #2
Moved thread to tech to tech chat.
-
12-06-2012, 04:05 PM #3
I think this exercise is trying to get you comfortable with these terms and how simple the solution actually is.
So lets start with a question. What is your understanding of what liquid subcooling is?
-
12-06-2012, 04:25 PM #4
Professional Member
- Join Date
- Nov 2012
- Location
- PA
- Posts
- 45
I think he is currently taking a test.
-
12-06-2012, 04:50 PM #5
Professional Member
- Join Date
- Feb 2012
- Location
- EVERYWHERE
- Posts
- 161
I think he failed a test.
-
12-06-2012, 05:24 PM #6
Do you just want the answer or do you want us to help you figure it out?
-
12-06-2012, 05:45 PM #7
Regular Guest
- Join Date
- Dec 2012
- Location
- nc
- Posts
- 7
100 degrees
-
12-07-2012, 09:01 AM #8
New Guest
- Join Date
- Dec 2012
- Posts
- 2
I thought 100 degrees was right but I wasnt sure. I was working on some review questions out of my book, and that one just had me totally stumped. Thanks everybody!
-
12-09-2012, 01:13 AM #9
TXV means you will get constant superheat ...
which means you want to fill the condenser just enough to guarantee a liquid seal at the metering device(txv)
110 - 10 = 100 degrees to get the manufacturers requirement.Economy - Quality - Speed <---- pick two