HVAC Student question about frozen evaporators
In class last night we were charging a very under charged system. While doing so, with the help of an aid instructor, the suction line was freezing up for quite some time and suddenly the unit kept short cycling and high side pressure kept surging up, then compressor would shut down, then once the pressure dropped it would cycle on again. I never got an answer to why this might be happening, however I suspect that the evaporator might have froze up, or that the metering device froze? Any input would be greatly appreciated.
-
12-06-2012, 12:26 PM #2
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,634
That system had two problems. Low load and a severe overcharge.
The low load was causing the freezing and the overcharge was causing over pressurization which was why your high side pressure would surge when the compressor started. Then It would shut off on the overload or high pressure switch if it has one.
Did you measure superheat and subcooling?
-
12-06-2012, 12:42 PM #3
Sure sounds like it was cycling on one of the safeties. What were the pressures? Also any superheat/sub cool numbers would be helpful. Also maybe what the equipment was.
If it was the low pressure switch and you were indeed severely low on charge that would explain a lot. Just because you are adding and your gauges read 100 psi (making that up) doesn't mean that's what your pressure switch is really seeing.
-
12-06-2012, 12:56 PM #4
The big question is did it get solved? If not why not?