Thread: Trane Comm 4 Infocon driver
12-05-2012, 04:10 PM #1
- Oct 2005
- 309
We have a number of Trane Comm 4 VAVs monitored from a JACE with the Infocon driver. The owner says that when they change a min air flow setting, they later see it revert back and often go to zero, instead of staying where they set it. Anyone familiar with this issue either as a Trane problem or an Infocon driver problem?
12-05-2012, 07:08 PM #2
- May 2004
- SE Pennsylvania
- 508
Are they setting the minimum airflow setting too low? If I remember correctly there is a minimum setting allowed based on the percentage of the max airflow setting. Zero may be acceptable and may be why it is changing to zero.
12-05-2012, 11:06 PM #3
- Oct 2005
- 309
They were actually trying to raise the minimum, so that doesn't sound like the problem, but thanks for the idea.
12-06-2012, 02:48 PM #4
- Nov 2012
- 10
I had ran into this same issue. I had found that the actual point in the Andover programming was programmed as though it was a sensor input on the device. This must be an Andover standard way of programming these flow rates. I'm not sure if this allows for a field calibration??? Anyways, our work around was to get into the programming for each controllers MinFlowSetpt and adjust the range on this point. It would allow us to command this value within the range that is set.
12-06-2012, 08:20 PM #5
Andover?
Propagating the formula. http://www.noagendashow.com/