Results 1 to 5 of 5
  1. #1
    Join Date
    Oct 2005
    Posts
    334
    Post Likes

    Trane Comm 4 Infocon driver

    We have a number of Trane Comm 4 VAVs monitored from a JACE with the Infocon driver. The owner says that when they change a min air flow setting, they later see it revert back and often go to zero, instead of staying where they set it. Anyone familiar with this issue either as a Trane problem or an Infocon driver problem?

  2. #2
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    1,769
    Post Likes
    Are they setting the minimum airflow setting too low? If I remember correctly there is a minimum setting allowed based on the percentage of the max airflow setting. Zero may be acceptable and may be why it is changing to zero.

  3. #3
    Join Date
    Oct 2005
    Posts
    334
    Post Likes
    Thread Starter
    They were actually trying to raise the minimum, so that doesn't sound like the problem, but thanks for the idea.

  4. #4
    Join Date
    Nov 2012
    Posts
    10
    Post Likes
    I had ran into this same issue. I had found that the actual point in the Andover programming was programmed as though it was a sensor input on the device. This must be an Andover standard way of programming these flow rates. I'm not sure if this allows for a field calibration??? Anyways, our work around was to get into the programming for each controllers MinFlowSetpt and adjust the range on this point. It would allow us to command this value within the range that is set.

  5. #5
    Join Date
    Jan 2003
    Location
    USA
    Posts
    3,417
    Post Likes
    Andover?
    Propagating the formula. http://www.noagendashow.com/

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.