    Its hard to start a Trane

    I went out last week on a 2yr old Trane dual fuel system. We got the call cause the original Trane dealer went out of business and my coworkers wife is this lady's boss.
    So she tells me the hp never seemed to heat very well. The air coming from the vents seemed cool.
    I go around and find this.



    I flip disconnect to check cap. I find one leg still hot. Pull cover off disconnect and find one leg direct wired. Disconnect will now not reset. So I direct wire other leg and check operation.
    I find the fan motor going out. I get it moving but its slow. Looking at the fan motor I see its an aftermarket Wagner motor. Definitely not original.
    Check press and can tell its low on charge.
    I order the correct motor from Trane.
    HO says she has not had any work to it. Only called the original installer cause the hp didn't seem to heat well. He told her it was working fine.

    I went back out today. Replaced the disconnect and fan motor. I recover the remaining 4lbs. I weigh in the factory charge of 9lbs. and some dye to leak check.

    In cooling mode looks good. 23 degree TD. Can't remember press. It was cool out.

    Switch it to heat mode. Press 300/36. Discharge line 196. Return line 77-78 degrees. 76 other side of biflow drier. 6 degree temp rise. Outdoor txv freezing up.
    Going back with an outdoor txv and drier.
    Btw, I found the leak. The installer didn't get the line sealed at the indoor coil.

    Apparently he tried getting rid of all of his scrap copper. How many joints do you see?







    Found out later that not only did this dealer shut down, he skipped town on his debts.

    Who says hacks can't install Trane.

  2. #2
    Join Date
    Oct 2010
    Location
    The very humid south
    Posts
    707
    10 joints??? WOW!!!

  3. #3
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,212
    Quote Originally Posted by acsolutionsllc View Post
    10 joints??? WOW!!!
    I think he smoked all 10 of them.

  4. #4
    Join Date
    Dec 2011
    Location
    North Texas
    Posts
    660
    (insert obscenities)

  5. #5
    Join Date
    Feb 2006
    Location
    FL
    Posts
    565
    Im sure he purged while brazing all that.....

  6. #6
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    5,042
    Quote Originally Posted by jvillehvac View Post
    Im sure he purged while brazing all that.....
    I wonder what caused the TXV to clog
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  7. #7
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,595
    Lol what a Charlie Foxtrot. WTH.

  8. #8
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,212
    I forgot to mention that the ho was standing there when I took the pics.
    She asked if I was going to post the pics on the internet. I said yep. Gonna put them on the WOS. She told me to make sure I posted the guys name. I just grinned.

  9. #9
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,625
    Where can I get those copper extensions? and do they come pre swaged?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  10. #10
    Join Date
    May 2011
    Location
    tallahassee,fl
    Posts
    380
    Must have lost his pipe stretcher

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event