    Kitchen exhaust make-up air


    The 2009 IRC requires that any kitchen exhaust fan that is over 400 CFM have a make-up air system that is the same CFM as the kit exhaust fan....and the make up air is wired to come on when the kit exhaust fan comes on.

    I have a customer with a 48" wide GE Monogram gas cook top (6 burners) requiring, per GE, a 1200 CFM kitchen exhuast fan.

    Do any mfg's make such a fan (approx 1200 CFM) that can be wired to bring on a make up air system WHEN the kit exhaust fan is turned on? So far the GE monogram fan cannot be wired such that it will active a make-up air fan when it (the kitchen exhaust fan) is turned on.

    Any feedback on a mfg who makes such a fan would be appreciated.

  2. #2
    Join Date
    Mar 2011
    Long Beach, CA
    Post Likes
    It sounds like you just need and interlock, simply use an auxiliary contact mounted on the exhaust fan contactor.

    You may want to try Greenheck for a pre-wired control panel.