Results 1 to 4 of 4
Thread: MODBUS RS-485 cable???
-
12-04-2012, 02:43 PM #1
Regular Guest
- Join Date
- Apr 2008
- Location
- Northeast
- Posts
- 74
MODBUS RS-485 cable???
I am working on a project which requires MODBUS integration to Automatic Transfer Switches. I can't recall the ATS manufacturer but we were told that they recommend we use one of the following RS-485 cables:
Belden 89729
Belden 82729
Alpha 58902
I'm not sure about the last two yet but the cost for 1000' roll of Belden 89729 is over $3K
The Belden 89729 specs are shown below. Is there something special about this cable which may be critical for this vendor? I didn't believe there was anything special about MODBUS RS-485 cable. I'm looking for a MUCH cheaper replacement. Any help would be greatly appreciated. Thanks.
Description:
24 AWG stranded (7x32) TC conductors, plenum, foam FEP insulation, twisted pairs, individually shielded
w/Beldfoil® (100% coverage), 24 AWG stranded TC drain wire, overall fluorocopolymer jacket.
Physical Characteristics (Overall)
Conductor
AWG:
# Pairs AWG Stranding Conductor Material Dia. (mm)
2 24 7x32 TC - Tinned Copper 0.6096
Total Number of Conductors: 4
Insulation
Insulation Material:
Insulation Material Wall Thickness (mm)
FFEP - Foam Fluorinated Ethylene Propylene 0.483
Inner Shield
Inner Shield Material:
Inner Shield Trade Name Type Inner Shield Material Coverage (%)
Beldfoil® Tape Aluminum Foil-Polyester Tape 100
Inner Shield Drain Wire AWG:
AWG
24
Inner Shield Drain Wire Stranding: 7x32
Inner Shield Drain Wire Conductor Material: TC - Tinned Copper
Outer Jacket
Outer Jacket Material:
Outer Jacket Material Nom. Wall Thickness (mm)
PVDF - Fluorocopolymer 0.432
Overall Cable
Overall Nominal Diameter: 6.629 mm
Pair
Pair Color Code Chart:
Number Color
1 White/Blue & Blue/White
2 White/Orange & Orange/White
Mechanical Characteristics (Overall)
Operating Temperature Range: -70°C To +150°C
Bulk Cable Weight: 40.181 Kg/Km
Max. Recommended Pulling Tension: 146.791 N
Min. Bend Radius/Minor Axis: 69.850 mm
-
12-04-2012, 03:25 PM #2
Professional Member
- Join Date
- Feb 2005
- Location
- Edmonton, AB Canada
- Posts
- 520
Good day,
Ideally RS485 should have the following specs:
twisted-pair with an additional wire for Reference which does not need to be twisted
Characteristic Impedance (Zo): 100 to 200 ohms
Mutual capacitance <= 12.5 pF/Foot
Capacitance to Shield <= 60 pF/Foot.
Propagation velocity >= 60%
If the wire you select does not provide a spec for its Characteristic impedance then it is not a communication cable.
Will RS485 work with cables that do not meet the above specs? Sometimes... but will be site (background electrical noise), installation (daisy chained, stubs, cable length, etc), and equipment (how many devices, data rate, etc) specific.
Cheers,
Sam
-
12-05-2012, 12:23 PM #3
I would make calls to different wire manufactures/vendors and tell them you need bids for that type of cable or equivalent.
We normally run a 2 conductor cable, likely very similar to what your spec is calling for, when I first used it the cable made me think of coax cable. I know the stuff isn't cheap, but I'll try to get more details later if I can.
Doing a quick search
http://www.smartwire.com/PDF/042003.pdf - 4 conductor, but nowhere near the same FEP.
http://www.alliedelec.com/search/pro...x?SKU=70005779
http://www.automationdirect.com/adc/...ble_%28Bulk%29
http://www.mouser.com/Search/Product...iKMrhsRA%3D%3D
http://octopart.com/58902%2Bsl001-alpha%2Bwire-99025
http://www.alliedelec.com/search/pro...x?sku=70140522
http://www.markertek.com/Cables/Bulk...-8771000.xhtml"How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
BIG Government = More Dependents
http://threedevilskennel.com/ - not my website.
Versatile Hunting Dog Federation - www.vhdf.org/
-
12-05-2012, 12:55 PM #4
Siemens uses anixter cable.


Reply With Quote