Results 1 to 13 of 21
    May 2003
    El Paso, TX
    Hmm BUBBLES IN SIGHT GLASS
    Is it possible to have a correct charge and still have bubble in the sight glass? 8SH, 10 SC, R-22
    COOL
    Yes, especially with mixed refrigerants txv's and high loads.
    May 2003
    El Paso, TX
    What do you mean?
    especially with mixed refrigerants txv's?
    COOL
    Tallahassee, FL
    Bubbles in glass while sc is measured indicates noncondensibles.
    May 2002
    Possible non cons ....
    Do you have condensor fan cycling for head pressure control?
    This can also occur when the fan comes on after being off and is normal....
    mikeacman
    Quote Originally Posted by dukes13 View Post
    What do you mean?
    did I studder?
    May 2003
    El Paso, TX
    evacuate system down to 445!
    Quote Originally Posted by mikeacman View Post
    I jumped the switch to operate continuously,
    NO mixed refrigerants.
    COOL
    Oct 2011
    Chicagoland Area
    did I studder?
    Stuh-stuh-stuh-studder
    Nov 2012
    R-22 is not a mixed refrigerant. Subcooling is the cooling after in has become 100% liquid (no bubbles). I would check to make sure your readings are correct and possibly a restriction before the sight glass.
    Mar 2011
    Long Beach, CA
    What is the tonnage for this system.
    Is this a split system and if so how long is the line set.
    What is the the size of the liquid line and the suction line.
    Where is the sight glass located, is it at the condenser or at the evaporator.
    Does this system use a TXV.
    What is the suction pressure.
    What is the head pressure, out door ambient temperature, and indoor temperature.
    Where are you measuring super heat, at the evaporator or at the compressor.
    If you are measuring at the compressor, why is the superheat so low.
    Have you verified correct air flow.
    Like Mikeacman asked, what are you using for head pressure control.
    The presence of flash gas or bubbles in the sight glass is not an accurate indication of non condensables in the system. For this you will need to identify all other probabilities first. Such as a low ambient condition and cycling of condenser fan motors. You must raise your head pressure to around somewhere in the range of at least 200 PSIG or 105 deg liquid saturation temperature first............
    _______________________________
    Trouble shooting is not part of the repair.......understand the symptoms and you will find the solution.
    Quote Originally Posted by alcomech View Post
    This is the best answer.
    Kaufman county, Texas
    Generally speaking a TXV requires liquid to operate correctly.
    But as for having bubbles with a given SC, yes it happens. The refrigerant is in motion inside a working system, not like on a work-bench where 1 degree SC=pure liquid. I generally work on RTUs and do not get a clear and reliable sightglass until around 16 SC.
    "You boys are really making this thing harder than it has to be". Me
    I like having infraction points, it makes me feel like 'one of the guys'.
    "I am not here to rescue you, I am bringing you along for emergency rations" Quark.
    Service calls submitted after 3PM will be posted the next business day.
    I give free estimates [Wild Ass Guesses] over the phone.
    My front door is locked. For your personal protection.
    Mar 2009
    Mid-Mo
    Quote Originally Posted by Tool-Slinger View Post
    I've seen this on chillers with subcoolers on them. Seems like on those you get about 12 degrees before the thing clears. The first time I saw it I actually had 2 thermometers on there just to make sure I wasn't crazy.
