BUBBLES IN SIGHT GLASS
Is it possible to have a correct charge and still have bubble in the sight glass? 8ºSH, 10º SC, R-22
COOL
-
12-04-2012, 10:30 AM #2
Yes, especially with mixed refrigerants txv's and high loads.
-
12-04-2012, 10:36 AM #3
Professional Member*
- Join Date
- May 2003
- Location
- El Paso, TX
- Posts
- 150
What do you mean?
especially with mixed refrigerants txv's?COOL
-
12-04-2012, 10:36 AM #4
Bubbles in glass while sc is measured indicates noncondensibles.
-
12-04-2012, 10:50 AM #5
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
Possible non cons ....
Do you have condensor fan cycling for head pressure control?
This can also occur when the fan comes on after being off and is normal....mikeacman
-
12-04-2012, 10:54 AM #6
-
12-04-2012, 11:44 AM #7
Professional Member*
- Join Date
- May 2003
- Location
- El Paso, TX
- Posts
- 150
-
12-04-2012, 11:46 AM #8
-
12-04-2012, 06:51 PM #9
Professional Member
- Join Date
- Nov 2012
- Location
- PA
- Posts
- 40
R-22 is not a mixed refrigerant. Subcooling is the cooling after in has become 100% liquid (no bubbles). I would check to make sure your readings are correct and possibly a restriction before the sight glass.
-
12-04-2012, 09:54 PM #10
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 282
What is the tonnage for this system.
Is this a split system and if so how long is the line set.
What is the the size of the liquid line and the suction line.
Where is the sight glass located, is it at the condenser or at the evaporator.
Does this system use a TXV.
What is the suction pressure.
What is the head pressure, out door ambient temperature, and indoor temperature.
Where are you measuring super heat, at the evaporator or at the compressor.
If you are measuring at the compressor, why is the superheat so low.
Have you verified correct air flow.
Like Mikeacman asked, what are you using for head pressure control.
The presence of flash gas or bubbles in the sight glass is not an accurate indication of non condensables in the system. For this you will need to identify all other probabilities first. Such as a low ambient condition and cycling of condenser fan motors. You must raise your head pressure to around somewhere in the range of at least 200 PSIG or 105 deg liquid saturation temperature first............
_______________________________
Trouble shooting is not part of the repair.......understand the symptoms and you will find the solution.
-
12-05-2012, 06:06 AM #11
-
12-09-2012, 01:19 PM #12
Generally speaking a TXV requires liquid to operate correctly.
But as for having bubbles with a given SC, yes it happens. The refrigerant is in motion inside a working system, not like on a work-bench where 1 degree SC=pure liquid. I generally work on RTUs and do not get a clear and reliable sightglass until around 16 SC.I draw all my schematics in crayon now. If they cannot always be correct, they can at least be colorful.
Service calls submitted after 3PM will be posted the next business day.
I give free estimates [Wild Ass Guesses] over the phone.
I am not in business to make money from other people so that I can afford to work for you for free.
If the fall is over, mmmm let's say, 6 feet or so,.. I do not 'bounce' very well.
-
12-09-2012, 01:27 PM #13


Reply With Quote