Plugged dryer and cap tube on reach in
Attachment 332931 dryer looks like cement!Attachment 332941 these chunks were between the condenser and the dryer BEFORE the filter screen! Cap tube looked the same as the dryer for about 6-8 inches.
-
can't see the pictures.
But from the sounds of it...
Sounds like someone put in a lot of leak sealant into a system with moisture.
-
No pics???
sent from my Samsung Galaxy Note
Member of the "Work Exchange Program"
"Will work for knowledge"
"Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
A Einstein
-
POE after dirty cond coil or bad cond fan mtr cooked it? Way way too common.
-
I see the pics fine on my phone. Can you guys not see them?
-
I can't see the images.
It's just blue text that says "Attachment 332931" & "Attachment 332941"
When I click on it. It says it's an invalid attachment.
-
Take a pic of the phone a post it
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Liberalism-Ideas so good they mandate them
-
 let's try this again!
-
Looks like you got yourself a meth lab.
Never seen anything like that. Could that be the dessicant from the drier? Maybe something in the drier ruptured?
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Liberalism-Ideas so good they mandate them
-
 Originally Posted by 2sac
Looks like you got yourself a meth lab.
Lol! I poured a fair amount of beads out of the dryer that were loose. They weren't crumbly at all. The rocks in my hand were in between the dryer and condenser before the dryer screen so I can't imagine that material traveling through the cap tube, evap, comp, & condenser to accumulate there. Cap tube cleared up about 6-8" up. Also it was very dry, no sign of oil whatsoever. Compressor still running quiet though. It's a 134a system and the condenser had enough wool on it to knit a sweater!
-
-
A friend of mine had an employee of his working on a lawyer's package unit. He was changing out the compressor and installed the LL dryer on the hot gas line. It ran fine for 2 or 3 months before the dryer came apart inside and stopped up the system. The material in your system looks like desiccant beads to me.
-
That is what a drier that was working suppose to look like. It was asked to do more that's when the unit quit.