    please explain how it shuts off or operation

  2. #2
    Join Date
    Nov 2004
    Location
    Practically Canadian ehh.
    Posts
    675
    From RT-SVX10C-EN (Trane)



  3. #3
    Join Date
    Oct 2006
    Posts
    77
    That pretty much sums it up.
    Trane service, and Supertek65 fan club president, midwest chapter

  4. #4
    Join Date
    Oct 2001
    Posts
    6,945
    you want your MWUP setpoint to be just enough so as the work force comes in that(people,lights)heat generated in a TRUE VAV building will add to the heat,and the SP will be made and the cooling will take the day.watch your hi static SP(2"-3"above running SP)if the VAVs dont react quick enough to the VFD coming down from that 100% you might get a hi-static trip...all depends on the duct sensor location for the static reading.