    I am looking at purchasing a couple of 05' vintage 3,000 ton York chillers (mod# YDYFYBJ3-DCA) and according to the literature the tube counts are as follows:

    Evaporator: 183 - 0.035" Enhanced Copper Tubes
    Condenser: 262 - 0.035" CSL Enhanced Copper Tubes

    I was looking at scrapping them as it can be very difficult to place an end user for chillers of this size especially when I haven't been able to secure documentation of service records. To my way of thinking these tube counts can't be correct. That is what I would normally find in 300 ton chiller. I am also surprised that chillers of this vintage would have 0.035" wall thickness. If anything I would have expected the tubes to have thinner walls than normal.

    The operating weight of these things is 162,000 pounds a piece. Does anyone have any insight into this matter? I simply don't see any possible way that these tube counts could be correct.

    Thanks for your help,
    Joe

  2. #2
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Those numbers are a designation of tube type. It's not the quantity. I don't know if I have any YD literature. I'll check in the morning.

    By the way, you posted this in the wrong forum. Should be in the chiller open forum.

  3. #3
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,303
    Post Likes
    Thread relocated to the "Chiller" section of the site.

  4. #4
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    I haven't dug up any literature on the York YDs. Never saw one out on the West Coast. Anyway, tube wall thickness and material type can be ordered from the factory. Tubes could be ordered as copper or Cu-Ni. Wall thicknesses of .025", .028" or .035". I did look up the most recent YK parts and for the largest YK offered (as of 2010) had 1850 tubes in the evaporator, 2325 tubes in the condenser and 180 tubes in the sub-cooler for a total of 4355 tubes. Those shells are 14' long, so there is 60,970 feet of copper tube. We used to use approximately 1 lb./ft as a rule of thumb so in the largest YK shells you would have close to 60,000 lbs. of copper. Your mileage may vary.

  5. #5
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,993
    Post Likes
    on the Series A chiller, the YF evaporator has 2,004 tubes and the YB condenser has 2,496 with an additional 180 tubes in the subcooler and i see them as 18 feet long. the YF, with a 183 designation, is 0.035" wall and the YB, with a 262 designation, is also a 0.035" wall.....

    with KY definition of 1 lb/ft, there is over 168,000 lbs of copper in 2 chillers! party is at your house!
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  6. #6
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by jayguy
    with KY definition of 1 lb/ft, there is over 168,000 lbs of copper in 2 chillers! party is at your house!
    Yeah, Joe, don't forget to throw us a bone!

  7. #7
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,198
    Post Likes
    EYE SEA

  8. #8
    Join Date
    Dec 2003
    Location
    45th Parallel
    Posts
    969
    Post Likes
    WOO HOO!! Party's at Joes house, HEY, how do we get there?
    “If your work speaks for itself, don't interrupt.” ~Henry J. Kaiser

  9. #9
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,198
    Post Likes
    Quote Originally Posted by jayguy View Post
    on the Series A chiller, the YF evaporator has 2,004 tubes and the YB condenser has 2,496 with an additional 180 tubes in the subcooler and i see them as 18 feet long. the YF, with a 183 designation, is 0.035" wall and the YB, with a 262 designation, is also a 0.035" wall.....

    with KY definition of 1 lb/ft, there is over 168,000 lbs of copper in 2 chillers! party is at your house!

    Quick question ? How much do theses machines weigh, 84,000lbs each ,wow? That's just copper only.
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  10. #10
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by milkyway View Post
    Quick question ? How much do theses machines weigh, 84,000lbs each ,wow? That's just copper only.
    Read the first post of the thread...last paragraph.

  11. #11
    Join Date
    Oct 2015
    Location
    Rossville, Ga
    Posts
    5
    Post Likes
    Can anyone tell me the tube count for a York Model # YTC3D3C2-CMD, if you have the manual web address that would be appreciated as well. Thanks

  12. #12
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by Allie Rembert View Post
    Can anyone tell me the tube count for a York Model # YTC3D3C2-CMD, if you have the manual web address that would be appreciated as well. Thanks
    I found a parts list for Style E & F chillers (yours is a "D")and it shows the evaporator tube count as 296 and the condenser tube count as 342. The manual I used is FORM 160.46-RP1. The problem in finding old literature on the JCI website is that it's, well, old. York didn't start digitizing manuals until fairly late in the game (I want to say later than 1997.) They were in a process of digitizing all the older stuff when they were bought by Johnson Controls, so as you can imagine that program came to a complete halt.

    You can find literature at this web address.

  13. #13
    Join Date
    Oct 2015
    Location
    Rossville, Ga
    Posts
    5
    Post Likes
    Thank you for your help!

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.