    Quote Originally Posted by Joehvac25 View Post
    What do you think of this, no pump on boiler just out in system, keeps boiler temps high and system side low.
    Not sure if you can make it out

    Attachment 332861
    like chuck crj showed in his simple piping schematic, there is only one way to properly pipe a boiler, it is non- negoitable where to put pump, and spirovent, tank, and fill valve, etc. We do this on every boiler we changeout or install in new construction. To the op, that is a criminal picture of the piping, and will never eliminate air.

  2. #22
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Get a 5 gallon bucket fill it with water stick the end of a garden hose in it then connect the other end of hose to the drain valve on the boiler piping, turn on valve and keep end of hose submerged under water in bucket until no air bubbles are present, shut off drain valve and all air should be eliminated. An old timer showed me this trick after I changed a circulating pump and got air in the system with no bleeders and I tried for hours to get the air out, he came by and within 10 minutes he had it fixed, needless to say I felt like a dummy but il never forget it and have used it many times now. Hope this helps.

  3. #23
    Join Date
    Jan 2007
    Location
    NH
    Posts
    279
    Post Likes
    it hurts my eyes just to look at it.

  4. #24
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    God you guys are funny!

    Look at all the threaded pipe! Man, that thing looks worse than my copper work, and I'm a HACK (maybe i'll post pictures of my baxi's later).

    Can we move this to wall of shame?

    Liberty, Why do bad things happen to good people. I think Joe nailed it, perpetually cheep HO knows how to work every big hearted sap who walks in the door. Teach him how to purge his own system and tell him what it'll cost to NOT have to do that any more.

    This is a good reminder for us. If they don't let you clean up pipes, air ain't your problem from now on. It's amazing how people find money when you don't make their plea of poverty your problem.

  5. #25
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    I know its a pile of poo. I saw the old system and very little was done to the piping. The tech who installed it claimed to know everything about everything and was very good at some things but apparently not boilers... He very well could have put the pump or the vent/tank in the wrong place. Here's the question I have, how in the hell is the air getting in the system? Do you guys think its air that was never bled out during the installation that finally migrated to a point where it stopped the pump from circulating? There are no leaks in the piping in the mechanical room for sure.
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  6. #26
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    Quote Originally Posted by tedkidd View Post
    Liberty, Why do bad things happen to good people. I think Joe nailed it, perpetually cheep HO knows how to work every big hearted sap who walks in the door. Teach him how to purge his own system and tell him what it'll cost to NOT have to do that any more.

    This is a good reminder for us. If they don't let you clean up pipes, air ain't your problem from now on. It's amazing how people find money when you don't make their plea of poverty your problem.
    It sounds like we might have a case of installer baffoonery. Seems to me that the things Beenthere and Joehvac25 said about the pipe work would have amounted to an extra hour of work during the install to save me and the customer this damn headache. Seems to me if I don't personally know how to do it I'd better learn or leave it alone rather than trust anyone...
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  7. #27
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    Get a 5 gallon bucket fill it with water stick the end of a garden hose in it then connect the other end of hose to the drain valve on the boiler piping, turn on valve and keep end of hose submerged under water in bucket until no air bubbles are present, shut off drain valve and all air should be eliminated. An old timer showed me this trick after I changed a circulating pump and got air in the system with no bleeders and I tried for hours to get the air out, he came by and within 10 minutes he had it fixed, needless to say I felt like a dummy but il never forget it and have used it many times now. Hope this helps.
    Thanks, I actually thought of this on my own while I was there, believe it or not. I don't think it made the process faster but it made it easier to see when the bubbles have gone.
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  8. #28
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,427
    Post Likes
    Every day is a learning experience in this business. We all hope that we learn things as "cheaply" as possible, but reality is over the years there are the jobs that you loose money on while learning lessons. The measurement is: How much did I pay to attend that class? With that said.

    Decide if you're going to stand your ground as a professional or stand up for your profession. You replaced the boiler. Is the boiler functioning properly? Does it cycle on and off while maintaining the set temperature on the aquastat? Did you include in the wording of your proposal that it was the homeowner's choice to not replace any piping of the system beyond the minimal required to replace the old boiler?

    You've bought this customer whether you like it or not. Now how much more are you going to pay to keep them? If you go back and find a way around the mess to get the air out you'll miss the one and only chance to fix what's really wrong. What happens the next time there's a problem and this customer blames it on something you DID? In their mind it's something you did, they will never accept the fact that the problems they're having are due to something they got you not to do in the first place.

    This is all just my opinion and it's worth just that.

    First I would point out (and prove it) that your boiler (which is all they paid you for) is working perfectly and that it's their system that isn't. Make them take ownership of the issue.

    Make an offer to correct the problem for a price, being very wordy and careful to point out that every penny you'd be charging them is to replace or correct problems caused by the system that you connected to. Have it all in writing. You can price this fix at cost and write off the markup to education or if you had an original bid for doing it right in the first place offer to do the fix for that added amount.

    You can offer to remove your boiler and refund all their money. Explain that they can then use their original amount to hire someone else to install a different boiler. Find a way to very softly remind them that the boiler is not the problem, but the original piping that they own.

    You can bleed the system of the air that's trapped in it and then (good luck here) get them to sign off on the fact that this was a one time deal at no cost as part of the original installation, but any further issues with their heating system that are not specifically related to just the boiler itself will be charged at full service call rates. Remember, you didn't take ownership of the entire house just because you put a boiler in.

    No matter how you proceed you need to come away from this having learned there are many definitions of: Getting the job at all costs. There are times we come across jobs that the little voice says "RUN!!!!!" From the pictures....... this was one of them if they were not going to allow you the profit to do the job right the first time.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  9. #29
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Where is the air coming from? I'm assuming with 2 hours of purging and bleeding you had the system completely full of fresh water. Fresh water has lots of oxygen and other gases in it. Heat it up and all that air separates from the water and hangs out wherever it feels like it.

    Piped properly, that air comes out of solution and gets trapped and vented at the air eliminator. The pressure out in the rads stays higher due to proper pump placement and air stays in the water until it comes back to the lowest pressure zone, right at the boiler.

  10. #30
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Liberty, interesting and helpful thread, thanks for sharing.

    Firecontrol, awesome layout of options!

  11. #31
    Join Date
    Nov 2001
    Location
    Moose Jaw, Saskatchewan, Canada Occupation:Interprovincial Plumber, Commercial Gasfitter Interests:
    Posts
    2,415
    Post Likes
    Are there problems? Yes. Pump orientation is one. But guess what guys. That piping is not responsible for the air getting in the system. There are thousands of systems that pump into the boiler and into scoops. Guess what? They work. Is it ideal? No, but they still work. Pipe it like chuck shows and life is usually good.

    Check the expansion tank first. Then, I would offer to repipe the boiler room, no charge. Do it like chuck shows, add lots of isolation valves. Isoflanges on the pump, valves on both sides of the zone valves, a valve then a drain valve on the expansion tank, Supply and return on the boiler.

    Get rid of the di electrics on the pump.

    Make it look nice and make it easy to service.

    I'll bet he recommends you to other boiler owners.
    I love my job, but paydays Thursday

  12. #32
    Join Date
    Jan 2002
    Location
    Chicago area, Il.
    Posts
    675
    Post Likes
    I see one zone marked "basement". Is the basement zone an old radiant one, with copper in the concrete, or does any of the piping go into the concrete. If the answer is yes, then I will guarantee that there is a leak in the floor, which is where the air is coming from, either through the leak, or due to the constant introduction of water into the system, which brings oxygen/air into the system.

    Also, that air eliminator would work better if it was straight up and down. Being crooked is going to prevent the float from moving up and down and releasing the air.
    Hi, my name is Glenn, and I'm a Toolaholic!

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •