Results 1 to 13 of 32
Thread: Boiler System Air Issue
-
12-03-2012, 12:55 AM #1
Boiler System Air Issue
Hi Guys, we installed a Carrier boiler about a year ago and about 2 months after we got a no heat call. Came out and found that the system was full of air. The radiators have no bleeders. The return lines have spigots on them for bleeding. It was a straight change out with no funds available to re-do the piping. I bled all the air out which took 2 hours (no joke). Just got a call from the home owner again with the same issue. Somehow there is air getting into this system and the Honeywell Supervent is not getting rid of it. The old 50 year old boiler didn't have this issue. There was a shotty remodel done in the home, I'm wondering if they tied the domestic into the boiler lines somehow? Forgive me, boilers are not my specialty. Also, the Grudfos pump was set on Medium, I switched it to High in hopes that it might move the air to the eliminator better. Do you guys have any suggestions for me on this one?

America; first we fight for our freedom,
then we make laws to take it away.
-Alfred E Newman
-
12-03-2012, 06:14 AM #2
Are you pumping away from the expansion tank/air vent?
-
12-03-2012, 06:22 AM #3
Looks like the vent is piped up to a bypass. Won't get rid of air too well that way. What temp is the boiler high limit set to, and what PSIG is it running at.
Are the rads old seam rads, that were converted over to hot water.
-
12-03-2012, 06:23 AM #4
-
12-03-2012, 07:05 AM #5
Check the exp tank to see if its water logged, other than that I really can't tell what's going on because my pics are so small on my phone. Mabe the messed with the system and now your stuck bleeding it, sometimes that air takes some time to dislodge.
-
12-03-2012, 07:27 AM #6
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,089
that is seriously ugly. your air problems are due to the near boiler piping.
i know its the customers money, but like it or not its now your job to convince him to either live with it or pony up and have it done right.
get Houlihans book pumping away. great book, can read in an hour. it will open you eyes to the difference between good, bad and ugly near boiler pipingmy boss thinks its possible to repeal the laws of physics
-
12-03-2012, 01:58 PM #7
I believe its set at 125* and 20 PSI. I'm not exactly sure about the temp, I would have to look at it again. I don't even know what a rad is... A guy I had working for me did the installation.
America; first we fight for our freedom,
then we make laws to take it away.
-Alfred E Newman
-
12-03-2012, 02:01 PM #8
I know it looks like crap. It was either change out or lose the job which was clearly stated by the home owner. Why would the piping be causing air issues? Why did the old boiler work just fine with this piping?
America; first we fight for our freedom,
then we make laws to take it away.
-Alfred E Newman
-
12-03-2012, 02:05 PM #9
Yes, its tied into the supply side and all the water is not forced through the vent. There are 2 tees in the main supply that build this vent/expansion manifold. I was wondering how good of a job this configuration could do. Would adding another vent or re-doing this one help me?
America; first we fight for our freedom,
then we make laws to take it away.
-Alfred E Newman
-
12-03-2012, 02:48 PM #10
Do you have leaks anywhere? The tank is full it will lose pressure and take in air. Some systems are harder than others to get the air out. If you pump away from your air scoop the pressure drop will let the air out also. I would be looking for leaks or bad exp tank, air has to come from somewhere.
-
12-03-2012, 03:14 PM #11
Yes, it is the piping that is causing your air problems.
Read the book ch4man mentioned and pipe accordingly. You will not have air problems again.
-
12-03-2012, 04:43 PM #12
-
12-03-2012, 04:51 PM #13
Chuck and beenthere must have good eyes, everytime I look at the pic I feel like mine are going to bleed lol


Reply With Quote