Cold storage room evaporating coolers
I am in the process of *designing a cold storage room, where should I provide the disconnect switch for the evaporating coolers (2 nos) and lighting fixtures. Should it be inside the cold storage room or outside.*
-
12-03-2012, 06:12 AM #2
Moved to Refrigeration and ice making forum.
-
12-03-2012, 11:31 PM #3
Professional Member
- Join Date
- Sep 2004
- Location
- Phoenix, Arizona
- Posts
- 51
It can be inside or outside box. Evap coils will need a means of disconnect in any case for code. So a tech can work on unit while the power is turned off.
-
12-04-2012, 02:34 AM #4
Regular Guest
- Join Date
- Nov 2012
- Posts
- 15
My concern was, that DS put inside should not get effected with the moist environment inside. So no issues I suppose, one should go for weather proof ones I guess. Thanks anyway.
-
12-04-2012, 09:05 AM #5
Weatherproof are fine. Seperate disconnects for each coil and a seperate one for lighting.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
12-09-2012, 08:39 AM #6
Regular Guest
- Join Date
- Nov 2012
- Posts
- 15
Thanks 2sak
-
12-09-2012, 09:20 AM #7
Professional Member
- Join Date
- Jun 2009
- Location
- Garland, TX
- Posts
- 349
Actually, we have had a restaurant with this same setup and end up having an issue. Here's the scenario: Walk-in-cooler, two evaporators, each with a disconnect, but only one evaporator has the thermostat. So anytime they do inventory, they want to turn off the fans, but only on that side of the cooler. So when they turn off the slave evaporator, the refrigerant still flows through it since the solenoid is powered through the master evaporator. And naturally, they forget to turn the coil back on, until half a day later, and by then the thing is frozen solid. (Yes this has happened more than once.)
One solution would be to use a dual pole switch on the slave evaporator, and run the thermostat wire all the way from the master to the slave evaporator, (in series) through the 2nd pole of the switch, then back to the master, so that no matter which switch gets turned off, it will kill the solenoid. I'm sure there is probably a prettier solution too but I can't think of what it is...
(...well of course a single disconnect would solve this problem too, not sure if that is some electrical code or whatnot.)
-
12-09-2012, 02:09 PM #8
-
12-09-2012, 02:22 PM #9
-
12-09-2012, 11:13 PM #10
Professional Member
- Join Date
- Jun 2009
- Location
- Garland, TX
- Posts
- 349
That's exactly what they do now, since I bypassed both of the switches!! Either that or they turn off they single circuit breaker that shuts off both evaporators