11-30-2012, 08:36 PM #14
I've got a goodman doing the same thing. Except in both heating and cooling. Eager to see what you find
-
11-30-2012, 09:06 PM #15
Regular Guest
- Join Date
- Aug 2012
- Location
- NE wisconsin
- Posts
- 178
Was the charge weighed in at install? Once we started weighing the charge in at install the callbacks stopped, 410a is two different refrigerants and will lie to your guages for the first few hrs of runtime. You may also have a leak, hard to tell without the proper diagnostic tools.
-
12-01-2012, 07:04 AM #16
-
12-01-2012, 07:30 AM #17
agree that weighing charge is the best option. never a callback.
-
12-01-2012, 07:42 AM #18
-
12-01-2012, 08:36 AM #19
Regular Guest
- Join Date
- Aug 2012
- Location
- NE wisconsin
- Posts
- 178
Not trying to start an argument beenthere, it was just the easiest way to put what I was trying to say. When a 410 a unit fixed orifice is installed and charged according to sh, it will be correct and something happens to the refrigerant that changes the pressures and temperatures. Weighing the charge according to the manufacturer specs eliminates that problem.
-
12-01-2012, 08:42 AM #20
Professional Member*
- Join Date
- May 2006
- Location
- Austin, Texas
- Posts
- 185
The refrigerant does not change. Maybe your indoor conditions change.
-
12-01-2012, 08:46 AM #21
I have to agree, 410 can be touchier on charging. Last summer I had a trane with EEV, new system start up. Let it run 15-20min to stablize, both SC & SH were off, LIke 3SC, 35 SH. Added and waited, press, SC & SH got closer but still off, added more, waited, better but still not right. Houra & 45 min later we looked good. Left the job a little after 5 PM. got a call around 9PM no cooling. Went back out, grossly overcharged. Adjusted it down into a recovery tank to where it would run and told them I would come back the next moring to finish adjusting. Had that happen to one of my techs also.
-
12-01-2012, 08:46 AM #22
-
12-01-2012, 11:19 AM #23
Professional Member
- Join Date
- Nov 2011
- Location
- Gerald, MO
- Posts
- 67
I appriciate everyones input on this. I think its high head pressure possibly the charge is off and the filter has not been changed.
-
12-01-2012, 12:03 PM #24
I'm going to take a stab in the dark, and say that you weighed this goodman in on startup.
Which would mean it's overcharged. Goodman is STILL overcharging their condensers from the factory. Unless I'm getting older stock. Who knows.
If you pull all your refrigerant out (or do a dry system), you can be on the money by weight. If you rely on the factory's 15' rule, your screwed.
Check your normal stuff. 2 month run time could be a filter.
I'm with beenthere on the gauges thing. Only time I've heard of that, is with microchannel package units. I think it was york that realeased that bulletin about their scrolls "losening up" after a few months of run time or something along those lines. If I'm confused, please enlighten me.
Still the idea 410a lying to you is confounded."Better tell the sandman to stay away, because we're gonna be workin on this one all night."
"Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."
"Just get it done son."
Dad adjusted
-
12-01-2012, 01:33 PM #25
Regular Guest
- Join Date
- Aug 2012
- Location
- NE wisconsin
- Posts
- 178
I've never had a problem topping off a system like you say beenthere, even on evaporator coil replacements, only on New system installs, it was explained to me that 410a is a mixture of two refrigerants and something happens to it after the first few hours of runtime. I can't explain it any better but with new installs if they are set to sh sc we always end up going back, weighed in it works so I will continue to set them up the way that avoids callbacks. I would really appreciate it if someone could explain it but I'm not too worried about it
-