    Whats the model and serial numbers and have you verified 24 volts between W and C? Also if it has an LED, what diagnostic code does it give? I wouldn't jump anything out until I verified what code is being given and that proper call for heat is being received at the board terminals.

  2. #15
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    3,424
    Pull the blower and inspect the heat exchanger on any 58PAV you come across - there's a good chance you needn't go any further.

    Most of the time you don't even need a mirror to find the cracks, only to get a better look and verify. Front of cells, 2nd bend upward, right at the dimple. I've found five or six so far and it's not even December 1 yet.

    Otherwise, this is a very simple furnace and easy to trouble shoot

  3. #16
    Join Date
    May 2011
    Posts
    79
    Quote Originally Posted by joeblo View Post
    If you jumper R to G and the fan switch on the thermostat is in the auto position the A/C cond will come on, this is normal. Disconnect the Y when doing this. The relay on the circuit board that turns the blower on is one of the most common failures I have seen with circuit board.
    Usually taking the form of the back of the circuit board being charred crispy under the relay. I think I've already replaced about a dozen BBQ'd single-stage Carrier circuit boards this month.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event