Results 1 to 13 of 17
11-29-2012, 10:30 AM #1
What is required to modify when using 407C and 404A as drop-in for R-22
HFC-407C and HFC-404A if they are used a drop-in replacement for R-22. Other then maybe changing the compressor oil out, are there any other requirements? Is this a cost effective then to buy R-22 currently, which may go up in price later on? I was just wondering about this and I wanted feedback from you guys.
11-29-2012, 03:48 PM #2
- Jun 2012
- 114
404a would probably require a new TXV at the least
11-29-2012, 05:56 PM #3
404 is just as expensive as 22
11-29-2012, 06:05 PM #4
Professional Member*
- Nov 2012
- Tahlequah OK
- 131
Why would want to use 404? It is really not a good replacement for 22 in AC system. I have never heard of using 404 in place of 22. 404 is always used in low temp systems.
11-29-2012, 06:13 PM #5
- Dec 2007
- Chandler AZ
- 165
11-29-2012, 06:33 PM #6
- Aug 2010
- Northern Cali
- 64
I pay alot more for 22 than I do 404. Never heard of dropping in 404 to replace 22.
11-30-2012, 06:40 AM #7
11-30-2012, 07:02 PM #8
hmmmmm... next junk R-22 unit you have, dump some 404 in it and report your findings lol.
11-30-2012, 07:26 PM #9
With a metering device change, r-22 to 404a is possible.
R404a is an excellent MT refrigerant. Don't think that it isn't. I haven't seen it in AC applications, though.
Besides oil changes and MD changes/modifications, you'll also want to replace any elastomeric seal on the system. The change from R-22 to 404/407 causes the seals to shrink back to a normal size and will VERY often cause VERY LARGE leaks.
12-01-2012, 07:08 AM #10
R404A would be suitable to replace R22 in a refrigeration application, but not a high temp one such as comfort cooling on an air to air system.
12-01-2012, 09:34 AM #11
- Jun 2003
- 3,641
That is a weird book you have In the pic. Neither of the refrigerants that are listed as "drop ins" actually are.
A "drop in" requires no modification to the system. Hot Shot is a drop in for r-12.
To replace R-22 with 404 would require at a minimum new TXVs, oil, and seals. It also has a pretty large capacity loss.
12-01-2012, 06:20 PM #12
12-01-2012, 06:32 PM #13
It is my school book. 'HVAC' NCCER Contren Learning Series . Currently in Level 3 book. One more to go afterward!
Well, thats why I asked the question here to get feedback from folks on the field. I also understood the "drop-in" as just charging the unit with replacement refrigerant and no need to modify. But as I continued to read the book, it said to change the oil in the compressor. And the pro's here also said other things like txv and some seals.