What is required to modify when using 407C and 404A as drop-in for R-22
HFC-407C and HFC-404A if they are used a drop-in replacement for R-22. Other then maybe changing the compressor oil out, are there any other requirements? Is this a cost effective then to buy R-22 currently, which may go up in price later on? I was just wondering about this and I wanted feedback from you guys.
wHen I diE I hOpe gOd haS mErcy oN my SiNful LifE
-
404a would probably require a new TXV at the least
-
404 is just as expensive as 22
-
Why would want to use 404? It is really not a good replacement for 22 in AC system. I have never heard of using 404 in place of 22. 404 is always used in low temp systems.
-
 Originally Posted by welling service
Why would want to use 404? It is really not a good replacement for 22 in AC system. I have never heard of using 404 in place of 22. 404 is always used in low temp systems.
A lot of med temp reach in use 404a
-
I pay alot more for 22 than I do 404. Never heard of dropping in 404 to replace 22.
-
 Originally Posted by MAC AIR
I pay alot more for 22 than I do 404. Never heard of dropping in 404 to replace 22.
I never heard of it either, loll but it says it in my textbook. I just wondering what you folks thought about it.
-
hmmmmm... next junk R-22 unit you have, dump some 404 in it and report your findings lol.
-
With a metering device change, r-22 to 404a is possible.
R404a is an excellent MT refrigerant. Don't think that it isn't. I haven't seen it in AC applications, though.
Besides oil changes and MD changes/modifications, you'll also want to replace any elastomeric seal on the system. The change from R-22 to 404/407 causes the seals to shrink back to a normal size and will VERY often cause VERY LARGE leaks.
-
R404A would be suitable to replace R22 in a refrigeration application, but not a high temp one such as comfort cooling on an air to air system.
-
That is a weird book you have In the pic. Neither of the refrigerants that are listed as "drop ins" actually are.
A "drop in" requires no modification to the system. Hot Shot is a drop in for r-12.
To replace R-22 with 404 would require at a minimum new TXVs, oil, and seals. It also has a pretty large capacity loss.
-
 Originally Posted by beenthere
R404A would be suitable to replace R22 in a refrigeration application, but not a high temp one such as comfort cooling on an air to air system.
What type of refrigeration application? And also when you say comfort cooling , you mean just plain AC units ? Thanks for the replies.
-
 Originally Posted by craig1
That is a weird book you have In the pic. Neither of the refrigerants that are listed as "drop ins" actually are.
A "drop in" requires no modification to the system. Hot Shot is a drop in for r-12.
To replace R-22 with 404 would require at a minimum new TXVs, oil, and seals. It also has a pretty large capacity loss.
It is my school book. 'HVAC' NCCER Contren Learning Series . Currently in Level 3 book. One more to go afterward!
Well, thats why I asked the question here to get feedback from folks on the field. I also understood the "drop-in" as just charging the unit with replacement refrigerant and no need to modify. But as I continued to read the book, it said to change the oil in the compressor. And the pro's here also said other things like txv and some seals.