Results 1 to 6 of 6
  1. #1

    Carrier / Bryant Draft Inducer Motor 318984753, 318984-753

    I have 10 year old furnace flame floats a litte going into heat exchanger. cycles out on flame senor..
    When i remove vent pipe flame flow normal.. Iam thinking new draft motor.

  2. #2
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    97
    I would be checking both side's of venting system before spending any money on inducer motor. imho

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    31,521
    Something very fishy. You can check the inducer wheel to see if crudded up. But I'd be looking at that heat exchanger awfully carefully too!

  4. #4
    Join Date
    Oct 2005
    Location
    B.C. Canada
    Posts
    435
    Quote Originally Posted by BaldLoonie View Post
    Something very fishy. You can check the inducer wheel to see if crudded up. But I'd be looking at that heat exchanger awfully carefully too!
    X2

  5. #5
    Quote Originally Posted by coolerik View Post
    X2
    X3

  6. #6
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    2,683
    X4