ID:	330981


the first 5 are this messed up install at a 12 year old building complex we service only for a few years, i guess i was the first one to notice that the draft was positive and vented out the side with that "powerventer" the paper was left behind for it and it say in bold letter NOT FOR SIDEWALL VENTILATION, i told by boss and he said that we cant really sell them on a new chimney because we gave them a contract, needless to say i was not the inspector for this contract. im scared to even go up there now. the boiler speaks for itself and the last is what i got out of burners on a gas p/m