    Doggy day care

    Happy Holidays, everyone! A client requested ventilation only for a dog daycare business, which I designed into a 1600 cfm exhaust fan, with 8' ceilings at 4 air changes per hour (this is a bit more than 4). He now requested air conditioning and heating as well. My question revolves around the best way to design this system. How should I choose equipment? Should I do what I initially thought as the solution: put a conventional gas furnace with ac and a separate exhaust with a fresh air louver in the wall and/or outside air in the return? or should I check into a makup air cooling/ ac? Customer expressed a low budget..... I am inspecting the design of another pet "resort" later today to see what others have done. Thanks in advance. cp

  2. #2
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Keep in mind all of the dog hair you will encounter when you do your design. How much ventilation does the customer need? I don't know why you would need 4 changes per hour. Only dogs live there. I would probably go with return air option with dampers and a low ambient stat to close the dampers in really cold weather. Low budget always makes me worry that I could be wasting my time.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    moved thread to tech to tech commercial



  4. #4
    Join Date
    Oct 2008
    Location
    ohio
    Posts
    18
    Post Likes
    How about a erv/ energy wheel we take care of a large pet resort all package units have a erv attached them

  5. #5
    Join Date
    Oct 2006
    Location
    houston
    Posts
    80
    Post Likes
    Get and install equipment where it is easy to clean

  6. #6
    Join Date
    Aug 2004
    Location
    Raynham, MA
    Posts
    125
    Post Likes
    Thread Starter
    thanks guys. I thought 4 ac/hr was the minimum. and up until yesterday, all he wanted was a quote on a ventilation system so my original design was that. but now he's gonna do it right, if he wants to hire me anyways. and yes, an air bear will be installed.

  7. #7
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Post Likes
    Figure out what your load calculation says you need and then upsize it with an ERV system. figure what kind of a load the animals may put on the system. Dogs don't sweat do they?

    Sent from my ERIS using Tapatalk 2

  8. #8
    Join Date
    May 2002
    Posts
    949
    Post Likes
    Erv unless his gas and electric meter have turbo bearings .

    It will pay for itself in a short time .

    Heating ,cooling ,humidifying ad dehuming all the outside air is gonna cost a fortune vs erv

    We take care of a large humane society . They have a sea of AAON erv units with heat/cool . if they just brought in outside air to make up for the exhaust required they would be closed due to energy costs....

    The units to do what you wish are available ...already made to go....

  9. #9
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    dont forget about dog piss. i service a doggy day care. evap coils falling apart. nasty stank smell

  10. #10
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    It is usually recommended that the dog kennel area's have 100% conditioned outside air as well as exhaust air. This area is usually kept separate from business office areas. In some instances there are separate rooms for observation that will not require 100% OSA, however some OSA and proper air changes per hour should be considered, along with the use of exhaust air so as to kept this room in a negative condition.

    As for the business area this should be designed as a separate conditioned space.

    I once did a 30,000 Sq Ft Animal campus located in the desert of Palm Spring, CA. which had radiant heat in the kennel area's in addition to heat and air conditioning with AAON 100% OSA units based on a 110 degree outside ambient air.

    You definitely should consider some sort of humidity control and hot gas bypass for low ambient conditions.

    As for a low budget, its difficult to put a price against comfort.

  11. #11
    Join Date
    Aug 2004
    Location
    Raynham, MA
    Posts
    125
    Post Likes
    Thread Starter

    Frown

    This client is really turning into One of those cheap ass guys that doesn't even want to do it nearly the way he's suppose to. He told me that he will be the only business that walks dogs every two hours, so urine wont be an issue, as a response to my suggesting specialized equipment. So after that, I conceded to quote him a standard system with two Lifebreath HRV's (I'm in Massachusetts), and now he wants me to quote him on just the a/c and a standard exhaust vent with a supply louver in the wall, which is what his drawing that he sent me was of . I guess I can either forget him, but I really need this job, or give him the Lifebreaths and a few minisplits with low ambient kits, just to get what I can out of him and then forget him too. the best business decision would be to stick to my guns or forget him, but I am starting up and really need this money. however I don't want to mess up so bad he has problems. I frickin hate dealin with cheap asses like this, but it seems like almost everyone is like that these days. why cant I find a nice client who wants it done right the first time and will pay a fair, but competitive price for it.... dammmmmmn it!

  12. #12
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Not only do they want it done cheap but they blame you for it not working like it would if done right. Sometimes it's best to walk away and let somebody else have the headache of trying to satisfy an unsatisfiable cheap customer.

  13. #13
    Join Date
    Aug 2004
    Location
    Raynham, MA
    Posts
    125
    Post Likes
    Thread Starter
    I agree. (wait for it....... ) BUT (yup, there it is) I am hurting for money and he needs this done. it's money waiting for someone, and I need it bad. I am borrowing gas money from my MOTHER !!! (should I admit that?).... simply put he needs to consider humidity no matter how he decides to do it. he knows he needs fresh air because of his insistence on ventilation,... Thanks for all the help guys. Happy Holidays, and MERRY CHRISTMAS TO ALL !!!

  14. #14
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    If that's the case, well I can understand your position then.

    You definitely need him to state his criteria in writing, and if possible have him provide a drawing along with specifications based on his requirements.

    After he has provided this information you can reply with a request for information which address and list your itemized concerns. Also per each concern, make you recommendations very short and in a direct manner. Do not list price for these items.

    Have him reply again in writing. You will then make a revision to you original quotation or estimate based on his input.

    Take his final decision and a simple drawing which you will submit for plan check and review at the city where this work is to be done, and hopefully with a stamped approval you can obtain a permit for the HVAC work based on his criteria.

    Have him agree to his own design and accept full responsibility for the performance of the HVAC system.

    Hope this helps.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •