    Oxygen vs Nitrogen Brazing
    In post dated 11/18/2012 titled Replacing Split System Heat Pump, professional member stated that nitrogen brazing should be used for a good install. Just found out that my HVAC contractor only uses oxygen/acetylene. Is this a problem?
    Jan 2005
    Emerald Coast
    Quote Originally Posted by jayp View Post
    It appears you got lost in translation.
    Oxy/acetylene is for the brazing & nitrogen to purge and prevent contamination
    inside the tubing.
    Just ask your contractor to purge (with nitrogen) while brazing.
    Do not attempt vast projects with
    half vast experience and ideas.
    Mar 2009
    Mount Holly, NC
    if they are ONLY using oxy/acet... they are doing you a disservice. all brazing should be done with trace amounts of Nitrogen or CO2 flowing through the tubing to prevent oxidation of the tubing from contaminating the oil and the expansion valve in your system.
    NEVER NEVER NEVER FLOW OXYGEN INTO REFRIGERANT LINES!!!!!
    The TRUE highest cost system is the system not installed properly...
    Find a HVAC-Talk Contractor by clicking here
    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?