Thread: problem with an older AAON unit form 1992

  1. #21
    Join Date
    Aug 2012
    Posts
    76
    Post Likes
    Thread Starter
    The unit did have small diameter stat wire that had been spliced in one spot originally installed. When i seen this i did change out the stat wire. I did check the voltage at the coil after the repairs were made and had 25 volts. The stat is about 40 to 50 feet away from the unit... i didnt see anything saying a minimum distance... do you remember what it was?

  2. #22
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    How many conductors do you have running to it?

    Here's the chart in the iom:
    200'= 20 ga
    350 =18
    500 =16
    750= 14
    1250= 12

  3. #23
    Join Date
    Aug 2012
    Posts
    76
    Post Likes
    Thread Starter
    there are 7 conductors

  4. #24
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    So 7 conductors and a 50' run would need 18 awg wire.

    7x50=350

  5. #25
    Join Date
    Aug 2012
    Posts
    76
    Post Likes
    Thread Starter
    well come to find out we have been there numerous times in the past replacing contactors... so this makes sense. I believe it was 20ga wire installed in the unit before i changed it. This would explain why the coils were burning out.

  6. #26
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Now you just have convince them to let you to fix it!

  7. #27
    Join Date
    Jul 2010
    Location
    South Florida
    Posts
    54
    Post Likes
    did you give them a unit replacement option? 21 year old unit will drain you of any profit u make on the repair.

  8. #28
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Aside from that issue, we don't have much trouble out of our older ones as we do on the newer ones.

  9. #29
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    Contractors may have been oversized over the years and are drawing more current to close.
    Multiple ways to fix the issue if so.

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •