Results 1 to 5 of 5
  1. #1
    Join Date
    Nov 2012
    Location
    Minnesota
    Posts
    124
    Post Likes

    York YCUJ Millenium Recip, Program FLA

    I got thrown on a mess for a new customer, His microboard was wrecked by salt water. He sent it out for repair and it was lost.
    He purchased and installed a new one with no EPROM. That is where I came in, bought him a new EPROM, set up dip switches and checked safety set points.
    Here is the question, How is FLA programmed into Microboard? I tried program+various York codes, 5144, 6144, ect. No luck.
    Unit is ready to go, even started it briefly but quickly shut it down do to buzzing starter (rusty armature) which customer is repairing.

    YCUJ660T8 46PA
    S/N RFEM6646AD

    Two compressor 136 FLA each

  2. #2
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    It has been a while since I saw one of these beasts, but my failing memory seems to recall the CT's had dip-switches that were set to RLA.
    If I am wrong it's because I'm senile, fragile somewhat hostile and not quite as agile as I once was.
    Ain't "None" of us as smart as "All" of us..

  3. #3
    Join Date
    Nov 2012
    Location
    Minnesota
    Posts
    124
    Post Likes
    Thread Starter
    That's what I thought, But it just has a single Ct with no dip switches, two wires to the pwr supply board?

  4. #4
    Join Date
    Feb 2010
    Location
    Russia
    Posts
    95
    Post Likes
    Quote Originally Posted by Chillrtech View Post
    Here is the question, How is FLA programmed into Microboard? I tried program+various York codes, 5144, 6144, ect. No luck.
    Try "YORK" on your mobile.

  5. #5
    Join Date
    Nov 2012
    Location
    Minnesota
    Posts
    124
    Post Likes
    Thread Starter
    I found the problem, there is no submenu on this panel. The FLA are set by a resistor on the power supply board J9 and J10, At least that's what York said.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.