Results 1 to 11 of 11
11-27-2012, 04:09 PM #1
- Nov 2012
- Montréal, QC
- 15
Tridium AX ModbusTCP to BACnetMSTP
Hello,
I have a heat pump with Gforce supervisor system and a Jace2.
The communication of HP is ModbusTCP and need translate the HP to BACnet MSTP
On the Jace, I created a BACnet network and a ModbusTCPSalve Network.
Questions are, after create all my Modbus Points (under Device->Points); Where can I create the virtual BACnet points? and Must I create a ServerPoints or I just need to create link between each points (Modbus -> BACnet) ?
Thx!
11-27-2012, 06:22 PM #2
You would create the points under the bacnet network/local device/export table.
11-27-2012, 07:00 PM #3
- Nov 2012
- Montréal, QC
- 15
Ok and after just a link between Modbus and BACnet point?
11-28-2012, 08:51 AM #4
- Jul 2008
- Seattle, WA
- 49
I don't know AX very well as I don't work on it much... But if you're just trying to do a straight network conversion maybe it'd be easier (and cheaper?) to do that with a FieldServer? I know you can get them to engineer your a solution preloaded if you don't know how to configure FieldServers, I've never gone that route so I don't know what it'd cost but from talking with other guys that seems to be a popular option.
11-28-2012, 11:11 AM #5
11-28-2012, 03:10 PM #6
- Nov 2012
- Montréal, QC
- 15
[QUOTE=noskilltech;14675321]You do not need a link when you export a point in the Bacnet Export Manager. You just discover the points you want to export and give them an AV or BV number.
Oh yeah Good!
But I can't write the BACnet point directly on Export Table (BACnet Writable: in1 to in16) but with other device or software, I will can discover and modify the BACnet point, right?
11-28-2012, 03:44 PM #7
- Dec 2004
- San Francisco Bay Area
- 435
Absolutely correct - once the point is exported from the BACnet Export Table, you can modify the points defined as writable from other devices or software. Just be sure to write to points at the priority levels you've defined (you can be selective, allowing writing only on certain priority levels, or can simply expose the writables at all priority levels).
12-01-2012, 05:25 PM #8
- Nov 2012
- Montréal, QC
- 15
Bad day!
I integrated my modbus Thermopump to BACnet MSTP, I can read all my BACnet point BUT I can't write on them with third software (Bacstage / Metasys / Orcaview), it's said like Write denied.
I created writable modbus point and after I selected BACnet point with all priority level.
Below the image:
Anyone have idea??
12-01-2012, 10:53 PM #9
- Jan 2007
- 156
The station automatically creates a user named BACnet. You need to assign the BACnet user operator write permissions to the BACnet export components.
Not everything that can be counted counts, and not every thing that counts can be counted - Albert Einstein
12-02-2012, 07:58 PM #10
- Nov 2012
- Montréal, QC
- 15
What is the link between the BACnet user with write permissions and the other BACnet software?
12-02-2012, 08:56 PM #11
- Jan 2007
- 156
Nothing really, as the client doesn't need to authenticate. It is just an added step in the station engineering to allow BACnet client devices to write to the exposed BACnet objects.
In Workbench hit ctrl + L, and paste in this link, local:|module://docBacnet/doc/aBACnetServerAccess.html .Not everything that can be counted counts, and not every thing that counts can be counted - Albert Einstein