Results 14 to 17 of 17
    Jun 2009
    Albuquerque NM
    Well I've been reading up on PID control and I think this problem is due the derivative part of the PID algorithm. From what I've learned, PID control can be the best but it appears that with thermostats, under certain conditions it can become unstable.
    Saint Joseph, MI
    If it's become unstable in it's control response, the issue is likely not the controller, it's probably something like thermostat location. Garbage in = garbage out. Maybe a water heater tuns on at that time creatign a negative draft that draws air into the wall cavity behind the thermostat, creating a draft across the temprature transmitter that creates a small shift in the local air currents. You'd be suprised. Always make sure any wall penetrations behind a thermostat are sealed. Poor thermostat location can cause a lot of issues. I've relocated on of mine for just that reason and need to relocate another that lcoated too far from the return duct and in a corner. I think the PO wanted it in a less conspicous location.
    Jun 2009
    Albuquerque NM
    That could be the case here. I was using a wired remote temperature sensor in an interior wall, which I have stopped using. It's possible that this wall could get cold inside. I'll check it out with my IR meter. The thermostat is also on an interior wall, but is closer to the returns than the remote sensor, so maybe air mixing is better there.
    Jun 2009
    Albuquerque NM
    Oh, and I see that the VisionPro uses P&I, not PID. Oops. But I"ll take a guess that it's continually adjusting the integral period. Maybe there's some lag there when the outdoor temp drops as fast as it does here at night.