    VisionPro IAQ thermostat - strange behavoir at midnight?

    I have a VisionPro IAQ thermostat and I've noticed this strange behavior twice in the last few days. I am running 3 CPH on heat. Right around midnight, it did 3 very short runs with very little OFF time between runs, during a period of about a half hour, and then resumed normal cycling at about 3 CPH. Load is about 50% at this time, so normally runs are about 10 minutes ON and 10 minutes OFF.
    11:56pm to 12:04am (8 minutes ON)
    1 minute OFF
    12:05am to 12:12am (7 minutes)
    3 minutes OFF
    12:15am to 12:23am (8 minutes)
    After this, it ran several cycles of about about 10 minutes OFF and 10 minutes ON.

    Is this strange or what?

  2. #2
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Did you feed it after midnight?

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Thats strange. Did you have any power outages during the day when this happened.

  4. #4
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    Have you checked the programming? Could there be any setback/setup changes within that 1/2 hour?

  5. #5
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Quote Originally Posted by kdean1 View Post
    Have you checked the programming? Could there be any setback/setup changes within that 1/2 hour?

    That was my thought. There's a couple of periods mashed in there.

  6. #6
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    Quote Originally Posted by motoguy128 View Post
    That was my thought. There's a couple of periods mashed in there.
    If two of us think so, then it must be right.

  7. #7
    Join Date
    Jun 2009
    Location
    Albuquerque NM
    Posts
    2,506
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Thats strange. Did you have any power outages during the day when this happened.
    Not that I know of. The first time I thought it was just a one-time thing, or maybe I imagined it. Then it happened again just like the first time.

    Quote Originally Posted by kdean1 View Post
    Have you checked the programming? Could there be any setback/setup changes within that 1/2 hour?
    I have all periods programmed for th same temps, and the "sleep" period starts at 10PM anyway.

  8. #8
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    Quote Originally Posted by garya505 View Post
    Not that I know of. The first time I thought it was just a one-time thing, or maybe I imagined it. Then it happened again just like the first time.



    I have all periods programmed for th same temps, and the "sleep" period starts at 10PM anyway.
    Maybe you have already done so, but I'd still check all 7 days on the program.

  9. #9
    Join Date
    May 2008
    Location
    Central Fla.
    Posts
    311
    Post Likes
    Do you have a back up generator? If so it maybe going through it's testing at that time and causing it to short cycle going into and coming out the testing due to loss of power.

  10. #10
    Join Date
    Jun 2009
    Location
    Albuquerque NM
    Posts
    2,506
    Post Likes
    Thread Starter
    No back up generator.

    I have a suspicion that this is caused by the weather here. We usually have a large day-to-night temperature difference. Since I have been watching the cycling behavior, I have noticed what appears to be some short cycling well before midnight, which seems to correct itself after a while. Could it be that the PID algorithm does not handle the large drop in temperature very well, and takes some time to adapt?

  11. #11
    Join Date
    Jun 2009
    Location
    Albuquerque NM
    Posts
    2,506
    Post Likes
    Thread Starter
    OK, there it goes again. 11PM
    10 min ON
    1 min OFF
    9 min ON
    1 min OFF
    3 min ON
    11 min OFF
    10 min ON
    15 min OFF

    Got any ideas?

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Looks like its trying to do 4 CPH. Set CPH to 2 and see if it still does strange cycles.

    Could be a faulty stat.

  13. #13
    Join Date
    Jun 2009
    Location
    Albuquerque NM
    Posts
    2,506
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Looks like its trying to do 4 CPH. Set CPH to 2 and see if it still does strange cycles.

    Could be a faulty stat.
    Yes, I was wondering about that, but it seems to work fine most of the time.

    Actually, the OFF times I listed above are all shorter than stated, by 90 seconds, because the furnace runs the blower for 90s after the call for heat ends.

  14. #14
    Join Date
    Jun 2009
    Location
    Albuquerque NM
    Posts
    2,506
    Post Likes
    Thread Starter
    Well I've been reading up on PID control and I think this problem is due the derivative part of the PID algorithm. From what I've learned, PID control can be the best but it appears that with thermostats, under certain conditions it can become unstable.

  15. #15
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    If it's become unstable in it's control response, the issue is likely not the controller, it's probably something like thermostat location. Garbage in = garbage out. Maybe a water heater tuns on at that time creatign a negative draft that draws air into the wall cavity behind the thermostat, creating a draft across the temprature transmitter that creates a small shift in the local air currents. You'd be suprised. Always make sure any wall penetrations behind a thermostat are sealed. Poor thermostat location can cause a lot of issues. I've relocated on of mine for just that reason and need to relocate another that lcoated too far from the return duct and in a corner. I think the PO wanted it in a less conspicous location.

  16. #16
    Join Date
    Jun 2009
    Location
    Albuquerque NM
    Posts
    2,506
    Post Likes
    Thread Starter
    Quote Originally Posted by motoguy128 View Post
    If it's become unstable in it's control response, the issue is likely not the controller, it's probably something like thermostat location. Garbage in = garbage out. Maybe a water heater tuns on at that time creatign a negative draft that draws air into the wall cavity behind the thermostat, creating a draft across the temprature transmitter that creates a small shift in the local air currents. You'd be suprised. Always make sure any wall penetrations behind a thermostat are sealed. Poor thermostat location can cause a lot of issues. I've relocated on of mine for just that reason and need to relocate another that lcoated too far from the return duct and in a corner. I think the PO wanted it in a less conspicous location.
    That could be the case here. I was using a wired remote temperature sensor in an interior wall, which I have stopped using. It's possible that this wall could get cold inside. I'll check it out with my IR meter. The thermostat is also on an interior wall, but is closer to the returns than the remote sensor, so maybe air mixing is better there.

  17. #17
    Join Date
    Jun 2009
    Location
    Albuquerque NM
    Posts
    2,506
    Post Likes
    Thread Starter
    Oh, and I see that the VisionPro uses P&I, not PID. Oops. But I"ll take a guess that it's continually adjusting the integral period. Maybe there's some lag there when the outdoor temp drops as fast as it does here at night.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •