Results 1 to 5 of 5
  1. #1
    Join Date
    Mar 2005
    Location
    Pacific Time Zone
    Posts
    4,422
    Post Likes

    Trane CVHE LON Info

    Anyone have a file that says what all the points are? I have nvi#'s and nvo#'s but cannot find a description to verify each.
    It's a CVHE-320 according to the prints.
    TIA
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    My 5 yr old son "Dad, Siri is not very smart when there's no internet."


  2. #2
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,882
    Post Likes
    Email send to address in profile.
    "There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria

    "It's not the customer's job to know what they want." -- Steve Jobs

  3. #3
    Join Date
    Mar 2005
    Location
    Pacific Time Zone
    Posts
    4,422
    Post Likes
    Thread Starter
    Here's all the info I can pull:
    nvi
    1 (switch), Chiller Ena
    2 (AI temp), Cool Setpt
    5 (%), Capacity Limit
    6 (HVAC Mode), Mode
    7 (AI invalid), Heat Stpt
    21 (AI invalid),BaseLdgSetpt
    22 (switch) BaseLdgReg
    nvo
    3 (switch), OnOff
    4 (temp), ActiveSetpt
    8-9 (%), ActualCap, CapLim
    10-13 (AI temp), LvgChW, EntChW, EntCndW, LvgCndW
    14 (string output), AlarmDescr
    15 (chlr status), ChillerStat
    23-24 (state), StatusOutputs, CprsrsRunning
    25-28 (switch) EvapWtrPum, EvapWtrFlow, CondWtrPump, CondWtrFlow
    29-30, 32-33, 37, 41, 49, 51 (AI invalid) Flow rates, SecTemps, Refrig Temps, Oil Temps
    31 (%) ActiveBLSetpt
    34-35, 38-39, 44-47 (AI in water) Refrig Press
    36, 40, 48, 50 (AI temp) EvapRfgtTempC1, CondRfgtTempC1, OilTempA, DischTempA
    58 (AI btu/hr) Unit Power
    Granted some of the values I could likely guess correctly, but I'd rather just know for sure.
    *Never mind, I just found it in NL220. Weird the front end doesn't pull the point details in...
    Last edited by crab master; 11-27-2012 at 08:44 AM. Reason: * and added descriptions found in NL220

  4. #4
    Join Date
    Jan 2008
    Location
    NY
    Posts
    158
    Post Likes
    On the Chiller I interfaced with, the chiller enable needed to be commanded to 0% to stop and 100% to start. Setting up as a binary did not work. This chiller had a UC800 display.

  5. #5
    Join Date
    Aug 2010
    Location
    Middle GA
    Posts
    104
    Post Likes
    All the Trane binarys are a 2 part SNVT. they require a true/false and also a %. You could write the % to 100 all the time and switch the binary on/off and it would accomplish the task.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.