    Anyone have a file that says what all the points are? I have nvi#'s and nvo#'s but cannot find a description to verify each.
    It's a CVHE-320 according to the prints.
    TIA
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    My 5 yr old son "Dad, Siri is not very smart when there's no internet."


  2. #2
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,738
    Post Likes
    Email send to address in profile.
    The first rule of any technology used in a business is that automation applied to an efficient operation will magnify the efficiency. The second is that automation applied to an inefficient operation will magnify the inefficiency. - Bill Gates

  3. #3
    Join Date
    Mar 2005
    Location
    Pacific Time Zone
    Posts
    4,332
    Post Likes
    Here's all the info I can pull:
    nvi
    1 (switch), Chiller Ena
    2 (AI temp), Cool Setpt
    5 (%), Capacity Limit
    6 (HVAC Mode), Mode
    7 (AI invalid), Heat Stpt
    21 (AI invalid),BaseLdgSetpt
    22 (switch) BaseLdgReg
    nvo
    3 (switch), OnOff
    4 (temp), ActiveSetpt
    8-9 (%), ActualCap, CapLim
    10-13 (AI temp), LvgChW, EntChW, EntCndW, LvgCndW
    14 (string output), AlarmDescr
    15 (chlr status), ChillerStat
    23-24 (state), StatusOutputs, CprsrsRunning
    25-28 (switch) EvapWtrPum, EvapWtrFlow, CondWtrPump, CondWtrFlow
    29-30, 32-33, 37, 41, 49, 51 (AI invalid) Flow rates, SecTemps, Refrig Temps, Oil Temps
    31 (%) ActiveBLSetpt
    34-35, 38-39, 44-47 (AI in water) Refrig Press
    36, 40, 48, 50 (AI temp) EvapRfgtTempC1, CondRfgtTempC1, OilTempA, DischTempA
    58 (AI btu/hr) Unit Power
    Granted some of the values I could likely guess correctly, but I'd rather just know for sure.
    *Never mind, I just found it in NL220. Weird the front end doesn't pull the point details in...
    Last edited by crab master; 11-27-2012 at 08:44 AM. Reason: * and added descriptions found in NL220

  4. #4
    Join Date
    Jan 2008
    Location
    NY
    Posts
    135
    Post Likes
    On the Chiller I interfaced with, the chiller enable needed to be commanded to 0% to stop and 100% to start. Setting up as a binary did not work. This chiller had a UC800 display.

  5. #5
    Join Date
    Aug 2010
    Location
    Middle GA
    Posts
    104
    Post Likes
    All the Trane binarys are a 2 part SNVT. they require a true/false and also a %. You could write the % to 100 all the time and switch the binary on/off and it would accomplish the task.