Vertical lengths ..... residential HVAC unit..
went out to look at a AC unit this fall .... customer is complaining that the AH runs continuously during the summer and get minimal cooling. Have check the coils on the AH, pressures on the compressor .... they were a little low but not too bad.... it is a 2tn unit but the vertical rise on the line set is at least 25 ft with 2 horizontal runs of 10 ft each. 2 tns is adequate for the cubic footage but I am trying to find some data as to whether or not these vertical runs are too excessive and some sizing adjustments.
The customer wants it fixed .... I am considering a Fujitsu split system I can mount on his back roof with two inside units.
any input would be appreciated ..... thanks
-
11-26-2012, 01:41 PM #2
Professional Member*
- Join Date
- May 2006
- Location
- Austin, Texas
- Posts
- 185
Check with manufacture for installation guides. 25' verticals are fairly common without any issues
-
11-26-2012, 02:24 PM #3
Regular Guest
- Join Date
- Aug 2012
- Location
- NE wisconsin
- Posts
- 176
Is the suction line 3/4? Like the last guy said check with the manufacturer, you may need to put in a 7/8 suction line.
-
11-26-2012, 03:39 PM #4
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,634
-
11-26-2012, 04:09 PM #5
Regular Guest
- Join Date
- Aug 2012
- Location
- NE wisconsin
- Posts
- 176
The overall length of 45 ft is why I was thinking increase dia. But there maybe other issues like airflow or dirty coil that are not readily apparent on a msg board. Check with the manufacturers specifications for long linesets, that will tell you exactly what size lineset you need as well if you need an oil trap or something like that.
-
11-27-2012, 05:37 AM #6Doesn't tell us much.a little low but not too bad
On a 25 foot rise to the air handler, your head pressure is 12.5 PSIG lower then at the condenser.
-
11-27-2012, 08:55 AM #7
Professional Member
- Join Date
- Sep 2008
- Posts
- 501
-
11-27-2012, 09:34 AM #8
The greatest pressure drop due to a vertical column of liquid occurs when the temperature of the refrigerant is the lowest.
The rule of thumb is assume a pressure drop of 0.5 psi for each foot of net liquid-line rise.
It is actually slightly less than this, about 0.48 psi/ft, for a liquid temp of 115ºf.Instead of learning the tricks of the trade, learn the trade.
-
11-27-2012, 04:30 PM #9