Results 1 to 3 of 3
  1. #1
    Join Date
    Nov 2012
    Location
    Upstate New York
    Posts
    6
    Post Likes

    Oil In refrigerant lines

    I just removed a residential 2.5 Tn compressor and air handler. I got over a pint of oil out of the refrigerant lines after I recovered the old R-22. The AH is in the basement with about 30 ft of line set. The AC was shutdown for the winter. I don't ever remember getting this much oil. This normal ??? or was the compressor failing ????

  2. #2
    Join Date
    May 2007
    Location
    Wildomar Ca
    Posts
    237
    Post Likes

    Angry Oil in refrigant l

    Quote Originally Posted by JimBE323 View Post
    I just removed a residential 2.5 Tn compressor and air handler. I got over a pint of oil out of the refrigerant lines after I recovered the old R-22. The AH is in the basement with about 30 ft of line set. The AC was shutdown for the winter. I don't ever remember getting this much oil. This normal ??? or was the compressor failing ????
    This could be caused by a dirty evap coil or running the a/ c at low temps.
    This causes inseffient oil return to the copressor.
    I wish this site had spell check.lol

  3. #3
    Join Date
    Nov 2012
    Location
    Upstate New York
    Posts
    6
    Post Likes
    Thread Starter
    Both the evap coil and the heat coil were filthy .... no access to the heat coil on this vertical AH. Customer tells me no service on the unit since it was installed almost 10 years ago. Thanks for the reply

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums