Results 1 to 6 of 6

Hybrid View

  1. #1
    Join Date
    Aug 2006
    Location
    Colorado
    Posts
    364
    Post Likes

    Confused Single Phase Scroll Going Backwards?

    So I diagnosed a leak in a system (small carrier rooftop, horizontal condenser fan), moved some of the parts to the identical system next to it to get some cooling in a computer room. A few weeks later the repairs were approved. I repaired the leak, installed a new blower motor, new dual capacitor, did the other stuff too. When I started it up with the refrigerant, the compressor made that 'backwards noise' and my pressures were equalized. I had to do a double take because I knew I saw suction in the initial diagnosis. So I shut it off, started it again and all was well. Has anyone seen this before on a single phase scroll? It has me scratching my head.

  2. #2
    Join Date
    Jan 2008
    Location
    Las Vegas, NV
    Posts
    81
    Post Likes
    Yes, I have seen it on some of the first gen scrolls. Early Carlyle Milleniums

  3. #3
    Join Date
    Aug 2006
    Location
    Colorado
    Posts
    364
    Post Likes
    Thread Starter
    Now that you mention it, I think that is what this was. It had two wires coming out of the top center. I guess it is a thermal overload? Any idea what causes the reverse?

  4. #4
    Join Date
    Apr 2001
    Location
    Over Here
    Posts
    1,104
    Post Likes
    Quote Originally Posted by tuba View Post
    Now that you mention it, I think that is what this was. It had two wires coming out of the top center. I guess it is a thermal overload? Any idea what causes the reverse?
    I understand the earlier generation of scrolls did not have a check-valve on the discharge. If the power 'hicupped' while the compressor was operating, the hot gas would back-flow, causing it to spin backwards, and re-start in reverse. Since the indoor t-stat would not satisfy due to a lack of refrigerant flow (cooling), the compressor would run continuously until the IO would open and shut the compressor down. It would then cool, and start back up with correct rotation.

    Another cause of the same problem is that top-mounted temp sensor in the compressor. A lot of Carrier TRA and YRA units with Copeland scrolls had them. The earlier scrolls used them, and they also hiccup the Y call when they fail. I've had to replace a few sensors that were opening prematurely. Those were 15-18 years ago or so, and they are old school nowadays.

    You happened to catch it at that magic moment.

  5. Likes eric1589 liked this post
  6. #5
    Join Date
    Aug 2006
    Location
    Colorado
    Posts
    364
    Post Likes
    Thread Starter
    Thanks for the comments. That is exactly how it sounds. I started it after adding most of the charge to the liquid side. I appreciate the responses, now I can stop scratching my head.....

  7. #6
    Join Date
    Jan 2008
    Location
    Las Vegas, NV
    Posts
    81
    Post Likes
    Yeah if it had the little sensor with two black wires out the top, that was first generation, If i remember correctly, It had to do with the scroll gears. If you added liquid into discharge side of comp during off cycle and then started it would spin backwards, once you shut it off and wait a few seconds and start it again it would spin correctly. I remember my first time....Good Times