Results 1 to 10 of 10

Thread: 200 AMP Jumper

  1. #1
    Join Date
    Aug 2008
    Posts
    214
    Post Likes

    200 AMP Jumper

    I was at a Customers house to replace a Gas Pack with a bad heat exchanger. The Unit sat close to the electric meter base. A while back the customer built a new Barn/Shop and the Power company put his meter at the road (200 Yards away) to cover both the Barn and the house. I couldn't help but notice the Jumpers that was put in the old meterbase with a clear cover. maybe a #8 wire at best.
    Attached Images Attached Images   

  2. #2
    Join Date
    Jun 2002
    Location
    south jersey
    Posts
    1,865
    Post Likes
    Looks a little bigger then 8 to me. None the less it is a cheap fuse. If there is a fire in the box you need a new fuse.
    You need to put the phone down and get back to work!

  3. #3
    Join Date
    Sep 2012
    Location
    Hebderson Ky
    Posts
    55
    Post Likes
    Name:  ImageUploadedByTapatalk1353519032.265237.jpg
Views: 790
Size:  51.4 KB
    That looks similar to this 20000 amp fuse I found on a pull out disconnect for a thirty amp a/c. Yes I swapped them out for actually fuses.

  4. #4
    Join Date
    Jun 2002
    Location
    south jersey
    Posts
    1,865
    Post Likes
    Good thing you swapped them. They were getting a little green probably going bad soon.
    You need to put the phone down and get back to work!

  5. #5
    Join Date
    Jun 2009
    Location
    Alberta, Canada
    Posts
    1,091
    Post Likes
    seriously, how expensive is a fuse???
    Have tools and gauges, will travel.
    ------------------------------------------------------


    RIDGID|YELLOW JACKET|UEI|TESTO|STANLEY|CPS|VETO| KLEIN|MILWAUKEE|MASTERCRAFT|

  6. #6
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    411
    Post Likes
    Ok I know a fuse holder should only have an appropriate fuse in it, but if the wire is the correct guage from the disconnect to the breaker box with the correct breaker in the box, how is so different from a non fused disconnect?

  7. #7
    Join Date
    Sep 2012
    Location
    Hebderson Ky
    Posts
    55
    Post Likes
    Well I agree on newer homes. This house originally had the old knob and tub wiring. It's had been up graded with a square d box but some of the circuits still utilize the old wiring which is stupid In my opinion. I didn't even charge them for the fuses covered it with the new system job number.

  8. #8
    Join Date
    Oct 2004
    Posts
    204
    Post Likes
    We see allot of older homes that have a 60 amp breaker with #6 wire going to the air handler with 10 kw heat...From there they junction 10 gauge wire going out to the condensing unit...In this particular scenario you must have a properly fused disconnect box going to the condensing unit period.

    Funny part is HVAC contractors in South Florida are not allowed to change out the disconnect box...yet I see licensed electricians install non-fused boxes in the above scenario 5 out of 10 times.
    It's all about heat transfer...

  9. #9
    Join Date
    Apr 2011
    Location
    Coastal Maine
    Posts
    1,092
    Post Likes
    Quote Originally Posted by qssfl View Post
    We see allot of older homes that have a 60 amp breaker with #6 wire going to the air handler with 10 kw heat...From there they junction 10 gauge wire going out to the condensing unit...In this particular scenario you must have a properly fused disconnect box going to the condensing unit period.

    Funny part is HVAC contractors in South Florida are not allowed to change out the disconnect box...yet I see licensed electricians install non-fused boxes in the above scenario 5 out of 10 times.
    Similar scenario here. We are not allowed to go any further than the equipment disconnect. A licensed electrician is responsible to set the disconnect and tie it into the panel. There have been more than a few instances where we have shown up to the site to set the condenser and we have refused due to the sloppy or code-violating work of the owner's electrician.

  10. #10
    Join Date
    Jun 2008
    Location
    va
    Posts
    802
    Post Likes
    Those jumpers you are refering to are actually meter jumpers. Many power co's use them in those situation. They are good for around a hundred amps. Even though it may be a 200 amp service, most services you won't see a hundred amps of current flow at all.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.