    Mcquay rooftop unit

    Had to check a mcquay rooftop unit model RPS, tries to start and goes out on flame failure. The maintenance guy says that it will only fire if he cover the inducer fan intake, anyone ever run into this, could it be a problem with the pilot tube?

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Pull the burner assembly. Could be pilot orifice, crossover tube, rotted brackets or a combination. Also could be a restrictor plate rotted out by the inducer.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. #3
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    You definitely want to check main gas pressure first. If a pressure regulator is used for medium pressure gas, verify that it is not locking up and on start up not opening completely. For this you will need a manometer.

    After that verify that manifold gas pressure is correct based on design.

    ________________________________________
    Trouble shooting is not part of the repair......understand the symptoms and you will find a solution.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •