    APC, Stulz, Data Aire... All are inferior to Liebert in my opinion.
    Also, in-row cooling designs are the way to go.
    LIEBERT IS THE CADILLAC OF CRITICAL ROOM COOLING!

  2. #15
    Join Date
    Mar 2012
    Location
    Georgia
    Posts
    21
    410a systems are even more prone to clogging LL driers.

  3. #16
    Join Date
    Mar 2012
    Location
    Georgia
    Posts
    21
    May have got away with it using 22, but never with 410 & POE oil. We fix a lot of these after poor install. Purge with nitro during all pipe work. Triple evac & use ACCURATE micron gauge.
    ONLY 2 things are meant to be in a working refrigeration system.....refrigerant & oil!